Of course 23kΩ allows 10mA to flow. That's how the figure 23kΩ is determined - from 10mA, a figure deemed not dangerous.
As I said, 23kΩ would result in a current of 10mA flowing (through a person)
IF the 'other metal' being touched were at 230V (and if one ignores the impedance of the person). However, as I also said, if the electrical installation as a whole is properly designed and constructed, it's very unlikely (theoretically 'impossible'?) that the potential of any exposed-c-ps or other metalwork could rise to anywhere near 230V for longer than it takes an RCD (ifpresent) to operate. Hence, as I said, in practice the current though a person may well be less than 10mA, and should persist for a significant time - hence probably pretty unlikely to result in a fatal shock.
The measurement is not going to be 22999 or 23001Ω. It will either be relatively low or very high, hopefully nearly infinite.
In most situations, that's probably true - but it's not inevitable. I have a particular 'issue' in some parts of my cellar, where the floor consists of (in many case cracked!) unglazed quarry tiles sitting on sand over soil (which can vary from 'bone dry' to 'waterlogged'). The resistance between a metal object sitting on that can vary from 'nearly infinite' (>500MΩ
after prolonged dry spells (e.g. summer 2011) to very low after prolonged wet spells (e.g. summer 2012!), when the water table is often higher than the cellar floor, and only the active drainage system prevents the whole cellar being submerged! ... and, of course, at various times, any resistance between those extremes.
I do not consider the concrete, in itself, to be a problem as concrete is, in any case, waterproof (unless, I suppose, very poorly made).
Yes, that's probably true - it's really when bolts etc. (or structural metalwork) pass through (or may pass through) or, as is quite common, if the concrete is cracked, that an issue may arise.
The likelihood of the bath becoming live by being touched by a live conductor is almost nil - especially if there are no conductors nearby.
Even with a cable underneath the chance of this happening is remotely small compared to a person touching a faulty appliance or cable whilst leaning on the bath or sitting on it using a faulty hair drier were it wrongly earthed - this would not be bonding. Bonding is a compromise and while it would be possible to think of a situation where had it been done differently a hazardous situation could have been avoided we cannot make an installation perfectly safe for all occurrences.
Exactly - and, as I wrote to Bernard, my personal view that, in this case, the 'compromise' (balancing of risks) is probably in favour of
not bonding the bath (or metal sink). ... as you go on to conclude ...
We can only do what is considered sufficient to avoid the more likely of many different hazards.
So, even if you perhaps thought otherwise, I don't think we're actually disagreeing about anything.
Kind Regards, John