No, but the supplementary bonding is for protection under fault conditions when the RCD will disconnect the supply.The thing is RCDs play no part in protecting from differing potentials across metalwork.
No, it's not. Supplimentary cross bonding is to ensure all metalwork is at the same potential.
What fault would rely on pipework?
Electrical equipment will be earthed in its own right, not protected by someone elses pipework and supplimentary bonding.
Supplementary bonding was (and still is unless certain regs are met) required to connect together all CPCs of circuits and all extraneous metalic parts within certain special locations such as bathrooms. The intention is to limit the voltage between parts when there is a fault.
If you have a nice earthy extraneous part such as a metallic bathtub connected via metal pipes and your electric shower faults you can end up with nigh on mains potential between the shower and the bathtub for the duration of the fault (up to 5s in the 16th edn regs for a water heater iirc), with wet naked bodies and a low resistance could be fatal. If you supplementary bond the two together then this potential difference is limited.
RCDs can be used to limit the duration of the fault which is one of the requirements of the 17th edn regs.