As has been explained, the regs explicitly require all cables to have a CPC
Where in the regs please john
As has been explained, the regs explicitly require all cables to have a CPC
http://www.csecables.com/acatalog/YY-Cable-5-Core-0-5mm2.html
Bluddy ell thats a good site! didn't know some of the .5 multicores existed
Thanks
Goodness - I missed that bit! I guess he means 'via the pipework'?Ooooh. That's not good. Is that why boiler commissioners insist on (cross) bonding all the pipes?Earth for the boiler comes via the main bond or not at all if its all plastic
I see that EFLI beat me to it - but 412.2.3.2 has been mentioned umpteen times already in this thread (mainly by EFLI and myself )Where in the regs please johnAs has been explained, the regs explicitly require all cables to have a CPC
I see that EFLI beat me to it - but 412.2.3.2 has been mentioned umpteen times already in this thread (mainly by EFLI and myself )Where in the regs please johnAs has been explained, the regs explicitly require all cables to have a CPC
Kind Regards, John
412.2.3.2 Except where Regulation 412.1.3 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory.
NOTE: This requirement is intended to take account of the possible replacement by the user of Class II equipment by Class I equipment
Of course (assuming that by 'over-sleeving' you mean just sleeved at the two ends of the bare conductor) that would mean that, for virtually all the run, the conductor would be only 'single insulated' (i.e. insulated but not sleeved) - which is an absolute no-no for any live conductor (outside of an enclosure) under any circumstances. The only 'single insulated' conductors allowed are G/Y insulated cables used as CPCs or bonding conductors.There was a mention of over-sleeving bare cpc, and used as a conductor. ... 100% not allowed under any circumstances according to the guy I spoke too at NIC.
I don't think there's much scope for interpretation. As has been explained, the regs explicitly require all cables to have a CPC (even if an earth is not currently required by whatever is connected to it), and there is no exception made for heating control cables. It sounds as if you probably should be using 5-core, not 4-core.
Kind Regards, John
I believe there is a reg that says you must have a CPC at every point?
Goodness - I missed that bit! I guess he means 'via the pipework'?Ooooh. That's not good. Is that why boiler commissioners insist on (cross) bonding all the pipes?Earth for the boiler comes via the main bond or not at all if its all plastic
In passing, I didn't know they made 'all plastic' boilers
Kind Regards, John
Not allowed and definitely unwise.Yes - via the pipework.
Obviously not allowed.No not plastic boilers but all plastic pipe. Ie boiler not earthed at all
As all boilers must be earthed that is not really relevant.There are a few boilers that need functional earths sao that makes oit interesting.
It is called 'supplementary' bonding and, if required - by measurement, not by looking at it - should connect simultaneously accessible extraneous and exposed conductive parts in a special location.Cross bonding is all to do with extronious metal in special locations.
No that is not the reason.Lots of boiler manu's state cross bonding not required ( only due to it being accomplished inside the boiler by other methods)
Please explain exactly what R17 is and what difference it makes to bonding.But that does not mean that the boilers that dont claim this do not need bonding ( as if they are running on pre R17 instalation - they certain ly will) ( but not reqired after R17)
In a way but only because of poor understanding and because judgements have to be made.Bonding & earthing - another lovely grey area!