I thought I hadn't made that many mistakes.
Would you quote 543.7.1.203(iii) and highlight where it says "circuit" in "circuit protective conductor"Since you seem so determined to miss the point (or are unable to grasp it) I'll give you a very precise answer to that.So is that a yes or no to the question ?
543.7.1.203(iii) requires two circuit protective conductors and those two conductors themselves individually need to meet the requirements of 543.7.1.203 which apply to circuit protective conductors.
Thank you.I agree that it does not.Do we agree that 543.7.1.203(iii) does not require either of those conductors, on it's own, to be a high integrity protective conductor as defined in 543.7.1 ?
True, but you seem to be implying that I'm a simpleton because your statement implies you do not believe there is a simple answer. If I were to write something that appears to be deliberately implying that you are a simpleton then I think you'd probably be offended.Only simpletons believe that "simple questions" always have "simple answers".Simple questions, that have simple yes or no answers.
Thank youGiven that the context of this topic is "Ring final circuits with high integrity earthing", no, of course notEDIT: So you agree that 543.7.1.203(iii) does not in any way require either of those conductors to be a ring ? Yes or No
This is where, IMO, it becomes irrational. Before I mentioned how the L and N were arranged (as a ring or not), you (and BAS) agreed that there were two CPCs, and you will presumably both continue agreeing with that if I tell you that it is a radial circuit, with the "two CPCs" being joined at the last socket. Why do those "two CPCs" (which, together, physically constitute 'a ring') suddenly become "one CPC" if one runs L&N conductors from the last socket back to the CU?Yes, one ring CPC.However, what I've been describing (after my second question) could just as easily be 'the protective bits' of a ring circuit.No, one if it were a ring circuit.Those "two CPCs"
That may be so but no more than why a ring circuit cpc has to be connected to the MET at both ends.This is where, IMO, it becomes irrational.
Because it is configured to the requirements of a ring circuit cpc.Before I mentioned how the L and N were arranged (as a ring or not), you (and BAS) agreed that there were two CPCs, and you will presumably both continue agreeing with that if I tell you that it is a radial circuit, with the "two CPCs" being joined at the last socket. Why do those "two CPCs" (which, together, physically constitute 'a ring') suddenly become "one CPC" if one runs L&N conductors from the last socket back to the CU?
This is where we disagree. What constitutes "A CPC" is defined in Part 2, which does not have a separate or different definition for "A ring CPC', and the definition of "A CPC" does not alter because of any regulations. If there are two 'sets of components' each of which qualifies as "A CPC" before they are joined, they can still be regarded as two CPCs when their ends are joined together - and that remains true regardless of how the L and N conductors in the circuit are arranged.And that's where everything falls apart for you, with a ring circuit. ... You have, as you say, created A ring CPC. In the singular. One ring. You have created a single CPC which complies with 543.2.9. 543.7.1.203(iii) requires that you have two individual ones, so you are no longer in compliance with that.It also satisfies 543.2.9, because by joining those two CPCs at the socket (every socket), one has created a ring.
Well, for a start, I'm not sure that one irrationality can be used to justify another! As I've said before, I agree that it's not obvious why there is a requirement for a ring final to have a ring CPC, but I suspect it may be a practical issue in terms of Zs. With 2.5mm² cable on a B32, one could not have a very long circuit if the CPC were connected to the MET only at one end.That may be so but no more than why a ring circuit cpc has to be connected to the MET at both ends.This is where, IMO, it becomes irrational.
That's not really an appropriate analogy, since, unlike the CPC situation, there is no situation is which either of the two halves could be described as "a horseshoe!Which of these meets the requirements of A horseshoe?
Fair enough...That's not really an appropriate analogy, since, unlike the CPC situation, there is no situation is which either of the two halves could be described as "a horseshoe!
You (and BAS) are talking as if the regs were well-written, unambiguous and crystal clear - in which case there would be no scope for discussion or debate - but there has been pages and pages of it! For example, just a short list in the regs of examples of the most common circuit arrangements which were acceptable as "HIE" would avoid the need for all this discussion/debate/uncertainty/whatever!Your view may very well be all that is required to achieve HIE for a ring circuit but it is not what the regulations say - for whatever reason(s).
Yes, but that's very different. In that case the regs are clear as to what is required, even if you personally think (maybe even 'know'!) that no harm would come from 'overloading' the fuse to that small extent for short periods of time. I am not attempting to 'over-ride' clear regulations - I am attempting to decide what unclear regulations "say", or are trying to say. Unsatisfactory, I know, but if the regs are unclear and even those who (jointly) publish them are "not authorised" to give advice on interpretation of them, what else can one do?I may very well judge that a 8.5kW shower will be alright on a 30A BS3036 fuse but it is not what the regulations state. Therefore I have to do something else.
Yes, but we haven't been talking about joining "two halves of a CPC" to make "one CPC" - we're talking about joining "two CPCs" and ending up with "one CPC" - the mathematical corner of my mind would be happy with "½ + ½ = 1", but is less happy with "1 + 1 = 1"Fair enough... ... .., but the point is that joining the two halves become one shoe.That's not really an appropriate analogy, since, unlike the CPC situation, there is no situation is which either of the two halves could be described as "a horseshoe!
You didn't.I'm sure I must have asked before, but don't recall getting an answer -
Obviously I never have but as with other rings I would install a radial.if a customer asked you to install an HIE ring final circuit, what would you do? Would you really install two independent CPC rings, 'walk away' from the job, or what?
Even when unclear, it comes down to how you and I interpret them.I am attempting to decide what unclear regulations "say", or are trying to say. Unsatisfactory, I know, but if the regs are unclear and even those who (jointly) publish them are "not authorised" to give advice on interpretation of them, what else can one do?
Lies ....You didn't.I'm sure I must have asked before, but don't recall getting an answer -
That's all true ..... If you are still undecided, what about turning it into a practical question - if a customer asked you to install a ring final circuit with high integrity earthing (the implication being that it should be regs-compliant), what would you do? I somehow doubt that you would install two separate CPC rings, or run a 10mm² CPC ring, would you?I am hesitant to vote (other than no) as .....
I'm not sure I fully understand that but, per my question, what would you do if the customer specifically wanted a ring final - walk away?Obviously I never have but as with other rings I would install a radial.if a customer asked you to install an HIE ring final circuit, what would you do? Would you really install two independent CPC rings, 'walk away' from the job, or what?
Of course - hence the extensive discussion!Even when unclear, it comes down to how you and I interpret them.
No - at least not primarily. If we were talking about views, based on knowledge and judgement, as to what would be electrically 'sensible'/'right'/adequate for HIE, I suspect that you and I, and probably even BAS, would essentially agree. What I am actually doing is try to use my knowledge and experience of reading, backed up by underlying knowledge about the electrical principles involved, to try to make a judgement about what the regulations are "saying", or trying to say.You are using your knowledge and judgement and deciding what you think is right.
With respect, I think that what both you and BAS are doing is interpreting what you believe they are saying, or trying to say.I am reading them and interpreting what they (actually) say.
543.7.1.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceeed 10mA, shall have a high integrity protective connection complying with one or more of the following:-Would you quote 543.7.1.203(iii) and highlight where it says "circuit" in "circuit protective conductor"
Is it an insult?True, but you seem to be implying that I'm a simpleton because your statement implies you do not believe there is a simple answer. If I were to write something that appears to be deliberately implying that you are a simpleton then I think you'd probably be offended.
I don't suppose you would like to apologise for that insult ?
You do realise that I was saying "no, of course not" to your question "So you agree that....", and not "no, of course 543.7.1.203(iii) does not in any way require either of those conductors to be a ring"?Thank youGiven that the context of this topic is "Ring final circuits with high integrity earthing", no, of course notEDIT: So you agree that 543.7.1.203(iii) does not in any way require either of those conductors to be a ring ? Yes or No
I meant - you didn't get an answer.Lies ....You didn't.I'm sure I must have asked before, but don't recall getting an answer -
Well, that's just asking the same question about what is a compliant ring.I'm not sure I fully understand that but, per my question, what would you do if the customer specifically wanted a ring final - walk away?
Yes, obviously and I believe that is what is written.]With respect, I think that what both you and BAS are doing is interpreting what you believe they are saying, or trying to say.
Because by running the L&N conductors back to the CU you have turned the circuit into a ring, and therefore created the need for the CPC to be a ring. So what had been a ring remains a ring. What had been a compliant HI protective connection for a radial (a CPC returned to the CU, thus forming a ring) does not remain a HI protective connection for a ring, because that needs two separate ring CPCs.Why do those "two CPCs" (which, together, physically constitute 'a ring') suddenly become "one CPC" if one runs L&N conductors from the last socket back to the CU?