Yes, I will claim that. "protective conductor (PE)" is not the same as "circuit protective conductor (cpc)". There are two different entries in the definitions - or hadn't you noticed that ?
Yes, I have noticed that.
I have not noticed, I must admit, 543.7.1.203 using the term "protective conductor (PE)". Is this because I've missed something which is there, or because you are seeing things which are not?
But I will tell you what I have noticed, and that is written English, which therefore construes as written English.
I have also noticed ".. every circuit .. shall have a .. protective conductor ..". So that makes it a circuit protective conductor.
cf:
".. every table .. shall have 4 legs ..". That will make them table legs.
".. roofs .. shall be covered with tiles ..". That will make them roof tiles.
".. drains .. shall be fitted with covers ..". That will make them drain covers.
Do you see? Or do you now want to start arguing against reading the regulations as if they were written in English?
Ah, the old diversionary tactic again.
Not so.
You know really well that the question I asked did have a simple answer
No - I know really well that it did not. I was unsure if you knew that, or if you were even familiar with the concept that what can be written as a simple question may not have a simple answer.
- just that you didn't want to give it. So you try and divert attention away from that by changing the topic. You do it a lot.
No, I was not diverting or changing the topic.
I was trying to show you that what can be written as a simple question may not have a simple answer.
Perhaps you could show where I've stated (or even implied) that every simple question must have a simple answer ?
You asked a question which you said had a simple, "yes or no" answer.
It did not.
So at the very least you were not recognising that not all "simple" questions have "simple" answers.
I'll again ask you a simple question:
"Simon, when did you stop beating your wife?". And I'll tell you that it is simple, and that it has a simple answer, which is the date you stopped.
Do you get it now?
So you are still saying that the words "Two individual protective conductors, each complying with the requirements of Section 543" includes the word "ring" or something with the same meaning ?
Yes -
something with the same meaning, which is the stated requirement to comply with the requirements of Section 543 which means a stated requirement to comply with the requirements of 543.2.9.
If you cannot highlight the word "ring" in that text then regulation 543.7.1.203(iii) does not require the PEs to be rings. There may be another eg which does - but it's not 543.7.1.203(iii)
You are being utterly ridiculous.
543.7.1.203(iii) requires compliance with Section 543.
Section 543 contains 543.2.9.
Therefore 543.7.1.203(iii) requires compliance with 543.2.9.
Therefore 543.7.1.203(iii) requires that each of the two individual cpcs of HIE ring circuits be rings themselves.
That's the way the regulations work.
Do you seriously expect me, or anybody else, to believe that you
really think that every single requirement for {thing T} has to be explicitly repeated every time a requirement for T is prescribed, and that unless this is done none of the others apply?
Do you
really think that if Regulation A1 says T must have property P1, and must comply with all the other regulations in Section A, and Section A has a Regulation A2, which says that T must have property P2, that if you've ticked the box for P1 you don't have to bother with P2 because A1 does not explicitly say that T must have P1 and P2?
Do you have any idea of how large and totally unusable the regulations would become if that were the case?
Please let us know if you do think that, because then we would all see that you have without doubt completely lost the plot, and we can all just ignore your barking mad ramblings.
Because that's what they are, even though you will no doubt try and portray that as an insult.
543.7.1.203(iii) does not require them to be rings because it doesn't explicitly say so even though it does explicitly say they have to comply with another regulation which explicitly requires that?
Sorry, but that really,
really is barking mad.
Do you agree that if for HIE for a radial circuit one has to double the normal number of paths from each socket to earth then it is common sense, logical etc that for HIE for a ring circuit one has to double the normal number of paths from each socket to earth?
No.
Fair enough.
What is logical is that if you have a circuit topology which has non-redundant connections, then something needs to be added to apply redundancy - ie a second path. If the circuit topology is such that redundancy is already present, then further redundancy is not necessary.
So you think it is logical that "high integrity" should mean "more integrity" for one sort of circuit but "same integrity" for another.
Fair enough.
Taking the specific example, would you compare the PE redundancy of a radial where the end earth connection has been extended and taken back to the MET thus closing a ring, and that of an RFC (with one cpc) ?
Of course.
With the former you have done something to increase the integrity. In the latter you have not.
Assuming both use the same termination methods - ie using separate terminals in both accessories and MET - is there any difference in either topology or redundancy between the resulting PE "rings" ?
No, there isn't. But in the former that topology represents increased integrity or redundancy compared to "normal", and in the latter it does not.
In the former it makes a change which makes it reasonable for there to be the concept of "high integrity" as something distinct from "normal", in the latter it does not. But the concept of "high integrity" as something distinct from "normal" is applied by the Regulations to RFCs.
If you are right, and that actually there are no such requirements, do you have a logical, simple even, explanation of why they didn't just exempt RFCs in 543.7?
Also consider the specific statement that (with some conditions relating to circuit protection) that where two radial circuits are present, it is acceptable to link the earth terminations of the end points together so that the CP forms a ring. That is most definitely not "doubling up" the number of CPCs
Indeed it is not. It is changing the topology to increase the redundancy of connections. If the circuit started out needing that level of redundancy then when you need to increase it you need to change the topology. The way which the regulations say that shall be done is to double up the number of cpcs.
It really does. That's what "two individual" means - two is double the number one.
[quoteSo we have two radials, lets assume wired in T&E, and by choice or design we arrange for the last devices to be in close proximity so we can easily just drop a bit of earth wire between them.
Do we now agree that both radials (subject to separate terminations etc) now meet the requirements for HI earthing ? And that this has a single ring of protective conductors from the MET, via all the accessories, and back to the MET ?[/QUOTE]
I agree that it meets the requirements for HI earthing for radials, not rings.