I see High Integrity meaning no chance of the earth failing. ( no as in zero +/- 0.00001 % ) How many joints ( loose teminals ) can occur before it is no longer High Integrity.
I think you're probably being a bit optimistic there - i's called
High integrity - not
Incredibly High integrity! [and, as a matter of detail, the 'chance' cannot be zero "+/-" anything - since you can't have a negative chance/probability!].
On a standard domestic ring failure if the CPC requires two failed connections.
I suppose that depends how you count 'failed connections'. If two CPCs go into a socket's terminal and it becomes loose, both may fall out simultaneously, leaving the socket with no earth connection.
On a radial it is one failed connection. Add the second CPC to the far end of the radial and it requires two failed conenctions. giving it the same "integrity" as a ring final.
Indeed, and that is the main point which has been discussed. I think that even BAS accepts that the radial with its CPC converted into a (one) ring is compliant as HIE, so (whatever the regulations "actually say") it makes no sense that the identical situation with a ring final would be unacceptable as HIE.
It is as much how the various CPCs are terminated in terminals as it is how many actual CPCs are in place. At the risk of being set on I would suggest that simple wrapping the CPCs together before putting them in the same terminal improves the integrity as there will still be continuity to other sockets if that terminal becomes loose.
If it's a ring, then all other sockets will retain their connections to earth, anyway - and, if one uses separate terminals (rather than what you suggest) without two separate faults (involving two terminals) even the socket in question will retain a connection to earth. With radials, it's obviously swings and roundabaouts - doing as you suggest makes it more likely that downstream sockets will retain their earth connections in the case of a fault, but increases the risk of the 'socket in question' losing it's earth connection.
It certainly isn't clear to some people who do electrical work as I have been told that if there are two earth terminals on a socket then they each must have ONE CPC and not two CPCs in one terminal.
For HIE, that is what is required.
Should one go as far as continuously testing the CPC loop is intact and then removing the power if the CPC loop becomes broken ?.
That (an 'earth monitoring system') is one of the options for HIE allowed in the regs.
If the situation / application requires High Integrity earthing then it is a special case and no set of regulations can specify exactly what has to be done in every situation. Common Sense has to be used together with knowledge and experience, especially as blind adherence to one person's interpretation of the regulations may make the situation more hazardous.
That's often true. However, in this particular case BAS's attempt to exercise "blind adherence" with wht he feels the regulations "actually say" would actually result in decreased hazard, since there would be four protective conductors (which he would call "two CPCs") connected to each socket in an HIE ring final circuit!