And 543.7.1.203 is a part of 543.7.1.
And 543.7.1.203 requires that circuits which have the characteristics which trigger the applicability of 543.7.2.201 be provided with high integrity protective connection which is one of:
(i) A single protective conductor ≥ 10mm²
(ii) A single protective conductor ≥ 4mm² with extra mechanical protection
(iii) Two individual protective conductors each complying with Section 543
[(iv) or (v) - provisions not relevant to this discussion]
So in the standard ring final with "separate terminals", which of 543.7.1.203 (i), (ii) or (iii) are you claiming compliance?
I'll turn that around to you.
Lets assume for a moment that you are correct, would you please state how the single YELLOW ring in your earlier diagrams meets 543.7.1 (specifically 543,7,1,203(iii)), and also how the single green ring in the same diagrams also meets 543.7.1 ?
Because, according to your logic, each of those rings must
on it's own meet the requirements of 543. And since you are adamant that a single ring cannot comply, then neither can either of your two rings individually. So each one, on it's own, must be two rings - so now a total of 4 rings. But then, each of those rings must
on it's own comply with 543, and therefore must be two separate rings - so now a total of 8 rings. I think we can all see where this is headed.
But you also have to consider something else. 543.7.2.201 could not be clearer. It says that "
A (note the singular) ... with a ring protective conductor ... is acceptable".
So at the very best, all you have proved is that the regs are not consistent within themselves.