I have a Gloworm Energysaver 60 boiler used in an s-plan open vent system. The system uses two Honeywell spring return zone valves for the HW and CH return pipes and a grundfos selectric pump. The boiler is in good condition and the the zone valves are both working correctly.
Recently I replaced the HW zone valve as it was stuck 'open'. I also took the opportunitty swap the the old gate valve that was being used as a fixed bypass valve across the boiler for a honeywell automatic bypass valve. Relevant manuals for my system below:
Boiler:
http://www.glow-worm.co.uk/stepone/data/downloads_sd/58/00/00/energysaver60.pdf
Pump:
http://www.screwfix.com/sfd/i/cat/pdfs/01/p3983301.pdf
Bypass Valve:
http://www.screwfix.com/sfd/i/cat/pdfs/50/p4734550.pdf
When the boiler is running, everything works fine and the sytem produces very little noise (just a reassuring hum). Once the water in the system is up to temperature, the boiler thermostat shuts down the burner and continues to run the pump (as it should). Again, this works fine and the system remains good and quiet.
However, when the cylinder and room thermostats shut the system down, the boiler starts to make quite a lot of noise. It sounds for all the world like popcorn being 'popped' in the boiler but, in fact, the noise seems to originate from the pump and simply echoes through the boiler.
When both the room and cylinder thermostats are 'off', both the CH and HW zone valves are obviously closed and the burner in the boiler is shut down. Immediately after the valve closes , the pump still runs (for about 5 mins) to help cool the boiler down a little (I guess). It is during this 5 mins that the noise can be heard.
In this mode, the bypass valve comes into action and opens up to allow water to circulate around the 4m of pipe that enclose the boiler, pump and bypass valve. Having tested the flow and return temperatures under these conditions, it appears that the valve is opening corrctly as the temperature around the whole loop is a constant 70 degrees (ie no temperature differential between send and return). For the record, when operating with the CH zone valve open, there is a normal 10 degree drop across the system.
I have adjusted the bypass valve setting from minimum up to about 0.5bar and the noise does not change. However, if I reduce the pump speed to minimum, the noise stops immediately. I guess the noise did not used to happen because the HW valve was stuck open so the water continued to circluate around the whole HW system all the time.
Since the water temperature is only 70 degrees and the noise stops when the pump stops, I'm pretty sure it's not kettling but I have no idea waht else it could be. Has anyone heard/seen anything like this before?
Cheers,
iep
Recently I replaced the HW zone valve as it was stuck 'open'. I also took the opportunitty swap the the old gate valve that was being used as a fixed bypass valve across the boiler for a honeywell automatic bypass valve. Relevant manuals for my system below:
Boiler:
http://www.glow-worm.co.uk/stepone/data/downloads_sd/58/00/00/energysaver60.pdf
Pump:
http://www.screwfix.com/sfd/i/cat/pdfs/01/p3983301.pdf
Bypass Valve:
http://www.screwfix.com/sfd/i/cat/pdfs/50/p4734550.pdf
When the boiler is running, everything works fine and the sytem produces very little noise (just a reassuring hum). Once the water in the system is up to temperature, the boiler thermostat shuts down the burner and continues to run the pump (as it should). Again, this works fine and the system remains good and quiet.
However, when the cylinder and room thermostats shut the system down, the boiler starts to make quite a lot of noise. It sounds for all the world like popcorn being 'popped' in the boiler but, in fact, the noise seems to originate from the pump and simply echoes through the boiler.
When both the room and cylinder thermostats are 'off', both the CH and HW zone valves are obviously closed and the burner in the boiler is shut down. Immediately after the valve closes , the pump still runs (for about 5 mins) to help cool the boiler down a little (I guess). It is during this 5 mins that the noise can be heard.
In this mode, the bypass valve comes into action and opens up to allow water to circulate around the 4m of pipe that enclose the boiler, pump and bypass valve. Having tested the flow and return temperatures under these conditions, it appears that the valve is opening corrctly as the temperature around the whole loop is a constant 70 degrees (ie no temperature differential between send and return). For the record, when operating with the CH zone valve open, there is a normal 10 degree drop across the system.
I have adjusted the bypass valve setting from minimum up to about 0.5bar and the noise does not change. However, if I reduce the pump speed to minimum, the noise stops immediately. I guess the noise did not used to happen because the HW valve was stuck open so the water continued to circluate around the whole HW system all the time.
Since the water temperature is only 70 degrees and the noise stops when the pump stops, I'm pretty sure it's not kettling but I have no idea waht else it could be. Has anyone heard/seen anything like this before?
Cheers,