LittlePlum2
Bypass in 22mm is wrong innit? should be 15mm, is that an auto bypassvalve I`m lookin at also?Might be worth getting someone in who has a clue friend maybe ask some questions of the `engineer` who fitted bypass.
No it's not my signature. I asked because you mentioned trying different pump speeds. A correctly balanced system will use a lower speed than an un-balanced one.Not sure if your 'Have you balanced the system?' question is actually part of your signature but, for the record, yes.
I can understand why you are suggesting that, but it may not be necessarily correct. It could be due to the fact that, now it is warmer(???), the radiators do not have to give off so much heat. The boiler is being controlled by the room thermostat, it never reaches the temperature set by the boiler thermostat. You could allow for this by turning the room thermostat right up so the boiler is running continuously while balancing. The boiler thermostat also needs to be at max.The only oddity I noted was that, even on pump speed 2, the temperature drop across the system (measured at the send return pipes of the boiler) was only 6 - 7 degrees. This suggests to me that the flow rate is too high.
At a 6°C differential the flow rate will be about 0.7 litre/sec (42/min). At that rate the boiler resistance is off the scale (see diagram 2.2 on page 8. But the pump would have to be on speed 3 to provide any head at that flow rate. This suggests something wrong: either the temperature measurement is incorrect or the boiler is not producing 17.58KW.JohnD, what you say makes sense to me and it also stops the popcorn noise (which is the real reason for this post). However, the manual for the pump states that, when in setting 1, the pump is not able to achieve the minimum flow for the boiler.
That's good - at least you are measuring off a surface with the same emissivity all the time.I'm using an IR thermometer and have attached matt black aluminium target plates (with lots of heat conductive paste) to the pipes to make for easier measurement.
I have not checked the gas rate of the boiler. Can this be done by watching the gas meter (providing the oven etc are off) or do I need a specialist tool?
Yes, you can check it by timing the gas meter. The calculation depends on your meter (cubic ft or cubic metres) and the calorific value of the gas, which will be on you gas bill.
Assuming the CV is 39MJ/m³, the flow rate will be 20.33/39= 0.52 litre/sec = 0.52 x 3.6 m³/hr. You use 20.33, which is the heat input to the boiler, when gas rating.
So if you time how long it takes for the right hand dial/red counter to make, say 2 or three revolutions you can easily work out the flow rate and convert this to kW input.
No probsCould you explain how you are calculating the temp drop/flow rate that you mention below. Apologies as I think I may have asked you this before (unfortunately, I can't seem to find the post).
Flow (litres/sec) = Output (kW) ÷ (4.18 x Temp diff)
4.18 is Joules constant aka the Mechanical Equivalent of Heat.
No, the boiler does not kettle at all. Provided that either or both of the zone valves are open, the boiler runs very quietly.
The issue is specifically limitted to the case where the cylinder and/or room thermostats switch the system off and the pump overrun function becomes active.