Sorry for my earlier, slightly intemperate, reply. I don't think the position I stated was wrong, but I could have stated it better.
Maybe I misunderstood, but I thought we were talking a hypothetical scenario in which the Earthing Conductor was disconnected from the provided 'earth (TN or TT) and, instead, connected to the incoming L feed. ... i.e. the MET and everything connected to it (including all CPCs, hence exposed-c-ps, and all bonded extraneopus-c-ps) would be connected to L, and nothing else in the building would have a path to earth (other than through the structure of the building)Depending on which conductor was actually cut, you could indeed. ... THE Earthing Conductor - supply to MET ... or the installation CPC - MET to CU. ...
If my above-mentioned understanding of the situation is/were correct, would you still regard what I have said as "strange".I think John's dismissal of the occurrence quite strange.
Everything you say is correct, but you are talking about something very different (and much more 'subtle') than what is being discussed here at an elementary level.Everything in a house has a potential. Everything you touch will result in current flowing between your finger and the object until you and the object are at the same potential. ... How much current ( Amp-Hours ) flows will depend on the capacities of you and the object and the initial potential difference between you and the object. ... Touch a spoon on a wooden table and current will flow to charge the spoon to the same potential as the body.
I was making the point that every metal object will create a current flow if touched by a person at a different potential. It is only a noticable effect when the charge on the item ( volts time cpacitance ) is large enough for a detectable current to flow.You are talking essentially about electrostatic phenomena,
Yes. As I said, it depends how strictly it meant THE earthing conductor and whether the vandals know what they are doing.Maybe I misunderstood, but I thought we were talking a hypothetical scenario in which the Earthing Conductor was disconnected from the provided 'earth (TN or TT) and, instead, connected to the incoming L feed. ...
the MET and everything connected to it (including all CPCs, hence exposed-c-ps, and all bonded extraneopus-c-ps) would be connected to L, and nothing else in the building would have a path to earth (other than through the structure of the building)
I just thought it strange you dismissed Penguin's suggestion so casually. It could be very dangerous.If my above-mentioned understanding of the situation is/were correct, would you still regard what I have said as "strange".
Yes. As I said, it depends how strictly it meant THE earthing conductor and whether the vandals know what they are doing.
The short bit from supply to MET could do what you say - namely:
However, the CPC from MET to CU disconnected from the MET and connected to live could leave all exposed-c-ps live and all extraneous-c-ps still connected to earth.
I just thought it strange you dismissed Penguin's suggestion so casually. It could be very dangerous.
I was making the point that every metal object will create a current flow if touched by a person at a different potential. It is only a noticable effect when the charge on the item ( volts time cpacitance ) is large enough for a detectable current to flow.
I based what I said on context. Penguin was talking about the possibility of malicious meddling in an external meter cabinet (see title of this thread). I was assuming that the MET, complete with its bonding connections to extraneous-c-ps, would be within the house (not the external box), in which case the only cable available (in the external box) for interference would be the true "Earthing Conductor" from incoming earth to the MET - and so I assumed that he was talking about the possibility of transfring that coinductor from the 'incoming earth' to teh incoming supply live/line.Yes. As I said, it depends how strictly it meant THE earthing conductor and whether the vandals know what they are doing. The short bit from supply to MET could do what you say - namely: ... However, the CPC from MET to CU disconnected from the MET and connected to live could leave all exposed-c-ps live and all extraneous-c-ps still connected to earth.
As above, perhaps I misunderstood what was being suggested (although I can't really see how). If my understanding was correct, then I think everything I said was reasonable, and not dangerous.I just thought it strange you dismissed Penguin's suggestion so casually. It could be very dangerous.
I'm glad his comments helped you. However, bear in mind that he was talking about potential differences due to things (people, spoons or whatever) having somehow become 'charged' with electricity, hence creating potential differences, but without their being electrical connections to anything. In that situation, if two things (one of which may be a person) touch, then a current will flow between them, for a tiny fraction of a second, until the potentials are equalised. It is the (usually) very brief duration of those currents due to electrostatic charging which means that they are usually not harmful (lightning is an obvious exception!)I thought it was quite a good way to explain potential difference, so thanks!
Someone is probably going to telly you that "electrocuted" means 'killed by electric shock' - so that one can't really have "seriously electrocuted" (a bit like "slightly pregnant"!).Yes, I get that. So, in a properly installed and functioning installation, what is the most likely cause for someone to be seriously electrocuted at home?
so an RCD wont save you from falling off a ladder.