I've never heard such nonsense as that of keeping PME and TT earths seperate as bernard seems so insistent on doing.
It was the DNO who installed my new supply last year who made the point very clear. My CPC ( PME ) must NOT have any connection to the CPC ( TT ground rod )of the adjacent shop ( from which my cottage had been supplied )
Hell the DNO actually deliberately connect the CNE conductor to an earth electrode at virtually every joint they make.
Yes they do in order to try and keep the neutral and CPCs derived from it as close to ground potential as possible. The difference in potential between them being generated by voltage drop along the neutral during the very common occurances of un-balanced loading on phases and occasionally due faults in the network.
It just goes to further reinforce the fact that bernard does not understand earthing and bonding.
I do understand that bonding is to keep all the bonded items at the same potential and "earthing" is either
( PME ) to provide a path for fault currents to reach the neutral without returning through an RCD sense coil and thus an un-balance is created which will trip the RCD
( TT ) to provide a path for fault currents to ground and thus to the star point of the sub station transformer.
If a number of items are bonded and one of them is also "earthed" then electrically all those items are connected to "earth" but the regulations and electricians who stick to those regulations seem to deny those items are earthed insisting they are only bonded.
If the OP upgrades to PME then he's got a proper earth to provide fault protection to the submains allowing him to ditch all the RCDs and the nusiance tripping they could cause, and just locally RCD protect the final circuits as and when neccessary.
A proper "earth" which could pull the steel armour to a voltage above ground via a path from the neutral ( which regulations say should be treated as live conductor ) which has no fuses in it to protect from excessive current.
If an installation has 30 mA or even 100 mA RCD protection fault currents to the CPC and earthed ( or bonded items ) will be limited to that small current because any higher and the RCD will be tripped. So why does the main bonding on incoming pipes have to be cable of such large cross sectional area ? Could heavy current cable be necessary for main bonds because if the CPC (derived from a faulty neutral) rose to a few volts above ground and one of the bonded service pipes had very low impedance to ground then the current in that bond cable could be several 10s or maybe hundreds of amps. ( Remember no fuse involved )
He can even just use PME earth to protect the SWAs and TT the outbuildings if he wants. This is a method I have used on farms before.
Where the regulations require isolation of the SWA ( earthed to the PME CPC ) from the CPC of the TT system.
I've never heard such nonsense as that of keeping PME and TT earths seperate as bernard seems so insistent on doing.
If they were connected then it would be exactly the same as a PME CPC in one house being connected to the TT CPC in the house next door.