For a ring final circuit you can calculate your Zs from the highest r1+r2 reading recorded.
Yes, I obviously understand that, but I was asking HOW you undertake the R1+R2 measurement. In particular, if it involves removing (and subsequently replacing) the CPCs from the earth bar, then, unless you subsequently undertake a ('live') Zs measurement, you theoretically can't be certain that the Zs has 'survived your fiddling in the CU'.
I would always Ze a TT supply of course as they can and do fail.
Yes, of course. However, I was asking whether you would normally 'bother' to undertake ('live') Zs measurements in a TT installation - since not only would it probably be 'unhelpful' (since, as we have both said, one cannot rely on incidental paths to earth remaining present) but, in a house like mine, it could yield some 'surprising' results.
I understand what you’re saying about Zs + Zdb will probably be lower than Zs + Ze, but it doesn’t actually matter. As long as your calculated worst case scenario values meet the minimum required value then you have proved the installation to be safe.
Yes, I agree with all that. However, I was really asking about the 'mechanics' of completing an EIC/EICR. Are you saying that, since it represents the 'worst case scenario' (i.e. the situation which would exist if all the bonded extraneous-c-ps were to disappear), you would record the 'calculated' Zs figures, even if you had measured Zs (and got somewhat lower answers).
In my opinion this is the proper way to prove the safety of your installation as the parallel paths of your bonding can not be relied upon - they could be removed by a neighbour tomorrow without your knowledge for example.
Exactly - which is why I asked whether you bother to measure Zs in a TT installation. One would hope that any TT installation is (like mine) designed not to rely on OPDs for fault protection (i.e. such protection is provided by RCDs), even if, 'at present', the loop impedances are such that it could.
However, one other thought about relying on 'calculated' loop impedances (i.e. from R1+R2 and Ze). Measurement of 'very small' resistances (like R1+R2) is a very iffy/unreliable business, and I imagine that Zs measurements (when it is current that is being measured) are probably much more reliable. For that reason, I suppose that, were it not for the potential 'safety' issues, the ideal would be to undertake ('live') Zs measurements with the bonding disconnected, rather than relying of R1+R2 measurements.
Kind Regards, John