What about when you are doing the R1+R2 test (on a ring final)?.... No need to disturb the earth bar once you’ve done your R1 + R2 test ...
Many installations are, of course, not 'modern', in that many will have at least some circuits which are not RCD protected. However, do you not trust the results of "low current loop testing"?On a modern installation every circuit will have RCD protection so you can only carry out low current loop testing anyway so there’s nothing to be gained.
Is that not potentially confusing/misleading? The standard Schedule of Test Results has, for each circuit', columns for 'maximum Zs', (R1+R2) and Zs, but not one for (R1+R2+Ze). It is therefore possible that ('measured') Zs figures could be recorded which were below the recorded 'maximum Zs' figure for the circuit, even though (R1+R2+Ze) is actually above that 'maximum'. That would probably not be immediately obvious from looking at the recorded figures.You can record either measured or calculated figures on the certificate.
You must be familiar with the experience that 'wiggling' the clips, or moving the tip of a probe around ('scraping' whatever it is touching) can result in an appreciable change in displayed readings. Admittedly, this phenomenon errs on the side of safety - since, whilst it is easily possible (by 'wiggling' etc.) to get a reading which is higher than the actual resistance, it's impossible (within the accuracy of the instrument) to get a reading lower than the actual resistance.What is iffy about low ohms testing? I have a calibrated meter which gives consistant results, and can be verified by calculating the estimated length of the cable run multiplied by the resistance per meter values of said cable.
Kind Regards, John