- C1 – There is a danger present, risk of injury and immediate remedial action required.
- C2 – There is a potential danger present and urgent remedial work is required.
I can only think of one thing which was low risk in 1992 which is a higher risk now, due to the advent of switch mode power supplies and rectifying the mains rather than isolating from the mains with a transformer first, with a TT installation today you need a type A RCD where in 1992 a type AC was good enough.
Then I struggle, I can see how using a 30 mA RCD is an improvement i.e. C3, but the lack of one does not make the installation dangerous.
I can see how use of plastic pipes may make an installation which was safe, less safe as a result, but it would have had the same effect in 1992 as today, be it less or more safe if you change something, then yes some thing can become dangerous, but is a Wylex fuse box was safe in 1992 unless something is altered it should still be safe today.
Best Practice Guide 4 issue 5 said:Non-compliances with the requirements of the current edition of BS 7671 that do not give rise to danger and do not require reporting.
The examples of C1 would have been just as dangerous in 1992 so no problems with that.
Some things one can understand, when plumbers started using thermal plastic header tanks then we needed extra protection, but only when a thermal plastic tank is fitted.
How can you say that in the same document that says lack of 30 mA RCD is dangerous.Best Practice Guide 4 issue 5 said:Consumer units having rewirable fuses can continue to provide satisfactory service
This is not the best ideaBest Practice Guide 4 issue 5 said:Inadequate number of socket-outlets. (Note: A Code C3 or, where appropriate C2, if extension leads run through doorways, walls or windows, or under carpets, or are otherwise being used in an unsafe manner).
However it can hardly be classed as dangerous either, it is on my to do list, but not very high, this
When the EICR was to tell the owner of work which it was desirable to do, then it did not really matter if coded C2 instead of C3, when a C2 can mean some one is homeless because the owner can't get it fixed within the allotted time, then it makes a big difference.
Using common sense if the ring finals are split so should one fail due for example an RCD tripping a cable would need running up or down the stairs that is to my mind far worse than a cable running protected under the door.
Which of course brings us back to the dates, in 1992 when we did not have RCD protection at 30 mA on socket circuits splitting the circuits up/down was no real problem, side to side or front to back was often better as a lower loop impedance, but it did not really matter, but when we add RCD's the chance of failure of the circuit increases, so once the RCD is added the risk of the occupant being forced to run cables up/down the stairs to keep essential supplies running increases, so then we get into the risk assessment, is the risk of tripping on a cable on the stairs higher than the risk of some live part being left exposed long enough for some one to touch.
Remember a RCD even at 30 mA does not stop you getting a shock, however it will limit it to 40 mS and likely trip in the case of a fault before you touch it.
Clearly the Electrical Safety Council can't make up their minds, and really are we after best practice, or just acceptable practice? And there is nothing about the types of RCD, if power line adaptors are used, should you give it a C2 unless a type F RCD is fitted?
Until putting the wrong code could make some one homeless I was not really worried if some one used the wrong one, but now it has become rather important.