I vaguely recall they specified a 45A fuse for my mates setup as well - but it's quite a few years since he got it. Needless to say, installing it was a case of "I've bought this, can you wire it in" rather than "will this work if I buy it" Now, where have we heard that before ?They recommend a 45A fuse but I suspect it will still be the same motor set up. Did MM charge for the modification?
Depends on which motor and why it's not running.What happens with this sort of compressor if only one of the motors works?
. Needless to say, installing it was a case of "I've bought this, can you wire it in" rather than "will this work if I buy it" Now, where have we heard that before ?
OK - just wondered if there were any risks associated with putting each motor on a different circuit.Depends on which motor and why it's not running.
I added a switch on my mate's unit to disable the second motor (just in series with the contactor coil) - when using a smaller amount of air, it's usually better to keep one compressor running full time (or more or less) than to have both keep starting and stopping.
From a mechanical POV, it's just two standard compressors sat on top of one receiver - each is standalone with it's own delivery pipe and non-return valve to the receiver. As long as it's unloaded properly, each could be started and stopped independently.
If one of the overloads trips then it depends. Tripping the overload on the first motor will stop the whole thing, tripping the second one will only stop the second motor. At least, IIRC - it's a good few years since I last had to do anything with it.
Obviously this only applies to the sort of unit the OP and my mate have - I'm sure there are more complicated industrial systems. On the latter, I would expect each unit to be effectively standalone, with a staging controller taking care of starting and stopping units according to demand.
Mechanically I don't think so - but it depends on whether they still have the same electrics.OK - just wondered if there were any risks associated with putting each motor on a different circuit.
Putting aside the issue that the supply authority should be informed of a inductive load of this size on a domestic supply....... *whistles*
If I was doing the Job, I think it would end up with a SPN switchfuse in the house, 16mm feed through the wall into the garage, then a type A distribution board in the garage (not a domestic consumer unit), Compressor supplied from 45A C type via a rotary isolator.
We are supposed to take account of manufacturers instructions, but point no. 8 goes against the grain with me!
You need someone who does commercial/industrial rather than just domestic only sparky (where are you in the country, there is a chance that someone might be able to recommend someone good in your area)
"Henleys" has become a generic name (like "Hoover" has for vacuum cleaner) for that sort of block - there are other makes.The tails going into the switch fuse split out with connector blocks (are they Henley blocks?)