A recent thread about the 'earthing conductor' in a TT installation has got me thinking ...
... in the absence of a functioning RCD (i.e. if there isn't one, or if it is faulty), does a ('standard domestic') TT earth electrode actually achieve anything? .. and that leads to the question of whether such 'earths' ever achieved anything in the days before RCDs (or VOELCBs).
Very few domestic TT electrodes have a low enough impedance to facilitate operation of even a 5/6A OPD in the event of an L-CPC fault, and certainly not for OPDs with higher ratings than that. Provided only that the building is properly constituted as an equipotential zone (i.e. any/all required main bonding is in place), I can't really see why the premises would be any safer (in the presence of an L-CPC fault) with a TT electrode connected than without it?
Am I missing something? If not, what was the thinking behind TT earthing in the pre-RCD/VOELCB days?
Kind Regards, John
... in the absence of a functioning RCD (i.e. if there isn't one, or if it is faulty), does a ('standard domestic') TT earth electrode actually achieve anything? .. and that leads to the question of whether such 'earths' ever achieved anything in the days before RCDs (or VOELCBs).
Very few domestic TT electrodes have a low enough impedance to facilitate operation of even a 5/6A OPD in the event of an L-CPC fault, and certainly not for OPDs with higher ratings than that. Provided only that the building is properly constituted as an equipotential zone (i.e. any/all required main bonding is in place), I can't really see why the premises would be any safer (in the presence of an L-CPC fault) with a TT electrode connected than without it?
Am I missing something? If not, what was the thinking behind TT earthing in the pre-RCD/VOELCB days?
Kind Regards, John