400V RMS but peak to peak will be 400 x √2 = 565V peak to peak I think,not √3....
Not quite. 400V RMS has a
peak of (400 x √ 2), as you say about 566V, but the
peak-to-peak would then be 1132V. However, we're not talking about either peak or peak-to-peak - all the figures being discussed are RMS.
...but its a long old time since I actually learnt any of that 3 phase theory so may be talking complete rubbish...
As above, almost correct (once you've doubled your answer to get peak-to-peak) - so not 'complete rubbish', although 'completely irrelevant'
What I'm talking about is the relationship between the RMS (or peak if you wanted) phase-neutral voltage and phase-phase voltage in a 3-phase supply. The latter is √ 3 times the former - hence,for example, the standard UK supply has a nominal voltage of 230V between each phase and neutral, but just under 400V (230 x √ 3) between any two phases. As I was saying, if there were 400V between each phase and neutral, the voltage between any two phases would then be (400 x √ 3), which is about 692.8V.
Kind Regards, John