I'm not talking about ratings, I'm talking about what happens with a star delta starter when it starts up. Initially the motor is connected star which has 230v applied across each coil, phase to the star point (400 / root 3).
It then switches to delta and each coil is connected directly to two phases each which is 400v per coil.
All figures I quoted are RMS.
It's your description that's confusing spark123 (I'm not saying it's incorrect)
Yes if you were to measure between each phase and the star point you would get 230v hence the common motor rating of 230/400
Which is why the star rating of the motor becomes 690v with 400v rated windings
But at the end of the day you are still feeding the motor with 3ph 400v
The rating of each winding never changes and is always the delta figure given on the plate
I presume (but obviously may be wrong) that it's meant to be (400 x √ 3) (i.e. the between-phase voltage of a 400V phase-N 3-phase supply) - but that should be about 692.8V, not 680V.Where does 680V come from??
Kind Regards, John
Edit: crucial missing bit added!
I think that is meant to be divided by, not multiplied by. For this very same reason your normal street 3 phase transformer gives out 400v between phases and 230v between each phase and neutral.
You are both correct,
Johns working out gives delta > star which he gave the correct answer to
Your working out is star > delta which also gave the correct answer
If you catch my drift
If one simply has a standard 230V/400V 3-phase supply, then, as has been said (amidst all the confusion!), the motor connection situation is incredibly simple. One starts with star connection, which gives 230V across each winding, and then switches to delta, which gives 400V across each winding. Full stop. All references to 680V/690V (or 400/690V 3-phase supplies) are then a completely irrelevant distraction, corresponding to nothing in the real world of a motor fed from a standard 230V/400V 3-phase supply.
Kind Regards, John
Not so John 400/690 rated motors are very relevant in the 230/400v real world as in every star/delta started motor you will come across and every large motor over 4 kw
Hardly a completely irrelevant distraction
3ph 690v supply's are used extensively offshore and in large industry too btw
Matt