Wow, Wikipedia is a wonderful thing...
Not wikipedia, just knowledge having worked in industrial control for many years
you have two identical motors under identical loads, one motor wired in star and the other in delta, which motor would have the lowest running current?
Delta
Star – high current, low speed
Delta – low current, high speed.
I think I know what you're trying to say but that statement is wrong on its own
In a star/delta starter, where do you put the overload?
Manufacturers vary, if it is put in the main power lines then it will set to FLC. If on the bottom of the main contactor then it will be set to FLC/1.73.
Anywhere else and there will be no O/L protection when in star and/or delta depending on location.