30metres, 5 kW.
Check your volt drop calcs
Think you’ll need 4mm minimum
Check your volt drop calcs
Think you’ll need 4mm minimum
... It can be laid on the surface just like the flex will become.
That's an option, but not compulsory. Armoured cable can be installed in many places, and unlike rubber flex it's designed to be used outdoors.I thought you had to bury SWA 450-600mm below the surface
I thought you had to bury SWA 450-600mm below the surface with sand and marker tape and all that stuff? Neither my back nor my wallet is up for that.
No it doesn't need to be buried, but it does need to be used/installed in a safe manner, ie not in a way that is likely to be a hazard to us or liable to it getting damaged.That's an option, but not compulsory. Armoured cable can be installed in many places, and unlike rubber flex it's designed to be used outdoors.
.Looks like your solution, don't forget to earth the armour if you still intend using plus/sockets.However, if it's okay to leave SWA on the surface, I'll do that (as I have about 20m of 3 core 6mm SWA in the garage)!
...don't forget to earth the armour if you still intend using plus/sockets.
They should not be a point of failure!If I'm leaving the SWA on the ground, I won't bother with plugs and sockets - they're just another point of failure and water ingress! .
They should not be a point of failure!
Properly installed SWA glands are designed not to allow water ingress.
They are designed to prevent water ingress into the enclosure to which they are attached, but do not (and are not designed to) prevent water ingress into the SWA from within the enclosure.They should not be a point of failure! Properly installed SWA glands are designed not to allow water ingress.
If that requirement applies to trailing sockets then surely that would mean that C13 and C15 and in fact pretty much every kind of detachable mains lead would be non-compliant.I think it's probably a ('male') 'power inlet' attached to the building that were talking about ..
... which presumably means that the need for shuttering/interlocking/whatever would relate to the trailing ('female') whatever-one calls-it - and, as you imply, such an animal may well not exist.
Kind Regards, John
In common-sense terms, perhaps yes, but not 'non-compliant with BS7671', since such trailing sockets and leads are not usually within the scope of BS7671.If that requirement applies to trailing sockets then surely that would mean that C13 and C15 and in fact pretty much every kind of detachable mains lead would be non-compliant.
And very much small child finger sized.In common-sense terms, perhaps yes, but not 'non-compliant with BS7671', since such trailing sockets and leads are not usually within the scope of BS7671.
However, of more interest/relevance are things like this (and modular variants thereof) which, if part of an electrical installation, would be within the scope of BS7671 and, if not shuttered, non-compliant with it.
View attachment 257507
Returning to common sense, the apertures of C13/C15 female connectors are pretty small, and one would certainly have to 'poke something small into it' to achieve contact with life parts. A 32A (or larger) female 60309 connector is perhaps a little more worrying, since the apertures are much larger, and the 'life parts' not all that deep within them.
Kind Regards, John
Quite. That's why I said "a little more worrying".And very much small child finger sized.
I promise it's hard work removing one from a screaming childs finger...Quite. That's why I said "a little more worrying".
However, in reality, I suspect that a 32A socket has too small an aperture for even the 'little finger' of a child.
Kind Regards, John
If they managed to get it in, I can well believe that.I promise it's hard work removing one from a screaming childs finger...
That sounds sensible. However, it's presumably when the female connector is not mated that it poses the greatest risk, isn't it?That's one of the bonuses of placing locks around mated connectors when they're in publics touch.