I wish I knew what the problem was.
Almost without a doubt, the Honeywell actuator has begun to jam/stick. I would though like someone to be able to confirm the actual valve spindle is only intended to rotate that 20 deg you mentioned earlier.
I wish I knew what the problem was.
Almost without a doubt, the Honeywell actuator has begun to jam/stick. I would though like someone to be able to confirm the actual valve spindle is only intended to rotate that 20 deg you mentioned earlier.
That is correct for that valveIndeed.
On reflection, it was probably more like 30-40 degrees, but no more, with the spindle hitting a definitive and solid 'stop' at the end of each travel, met with a fluid 'thunk' as flow stopped or opened, leaving me to feel this was 'correct'??
That is correct for that valve
I would tell you but according to you I "However, lacks the professionalism to enter a discussion without being offensive to other forum members."Thanks Ian, so it does just need a new head / actuator.
I would tell you but according to you I "However, lacks the professionalism to enter a discussion without being offensive to other forum members."
Read more: https://www.diynot.com/diy/threads/converting-to-combi-pipework.527086/page-2#ixzz5wIYvAJzS "
so guess what ?
And if it turned 360 deg it would be back in the exact same position that it started in, take a wild guess at why a Mid position valve is called just thatThe 20 degree turn doesn't sound right either, but perhaps others could comment on that? I would expect it to be reasonably free to be turned 360 deg.
Suddenly, the there is no hot water..........the boiler will not ignite, fire up
HazelFlorist, there is something you describe that that would not be caused by a faulty motorised valve:
Therefore, the boiler is not firing up when the hot water is set to be 'on' at the programmer and the cylinder thermostat is calling for heat. If you have a look at the basic wiring diagram I've posted below, you will see that the sequence of control of the hot water is:
Programmer switches hot water 'on', and is wired directly to the------>Cylinder Thermostat which also when 'on' is wired directly to the boiler ----------> Boiler switches 'on'
If you follow the circuit through, you will see that there is no electrical connection whatsoever via the motorised valve. So whatever position the motorised valve was in, the boiler would still fire up when the hot water was calling for heat. (and you tell us that it isn't)
View attachment 169361
If the valve was sticking in the 'heating only' position, the boiler would still heat up when the hot water was on, but the hot water would flow to the radiators instead of the hot water.
And if it turned 360 deg it would be back in the exact same position that it started in, take a wild guess at why a Mid position valve is called just that
.... therefore, and forgive my electronic ignorance, but could it be a faulty cylinder stat?
It's the original stat that was on the cylinder when the house was built in 1989 so is now 30 years old. Could it adopt a status that would stop it sending a signal to the boiler to fire up?
Equally often called a 3-port."MID" PORT!
The stat is just a simple switch, which is operated by temperature. As you sweep its setting knob across its range of settings, it should click on the way up and on the way down, at around the same setting, depending on the cylinder's temperature. The clicking doesn't guarantee it is working properly, but it would suggest it is. Likewise your room stat, should click as well, if its an old fashioned mechanical one.
Most likely point of failure, remains that 3-port valve actuator head.
I can only apologise for the poor signal to noise currently in this thread..