Guess what wire goes to the programmer terminal 1? Hint:
It won't be responsible for the "no hot water" that prompted your thread, but it would prevent the heating not working when the hot water wasn't on at the programmer. Terminal 1 of the programmer connects to the motorised valves grey wire and indicates that 'hot water is not required' (ie the programmer has switched the hot water off). As a result the valve winds to the heating only position and triggers the boiler if heating is required. If this wire is missing it wont do either.
That usually signifies that the contacts inside the programmer have worn out and not switching as they should.
A simple test, if you can do it safely would be to remove the programmer and add wire links between the terminals L, 3, & 4. as per below. Leave all of the other wires as they are.
View attachment 170064
This will replicate the heating and hot water being set to 'on' at the programmer. The room thermostat and cylinder thermostat should still work, so you can test the heating, and afterwards and set the thermostat low to prevent it staying on. Also, the hot water should heat up and once hot, the boiler will go off. However, don't do this test unless you can do it safely, because the programmer will remain disconnected, the live pins of the backplate will be exposed. If you do the test and everything works as it should, then you know that the programmer is faulty.
However, in the long term, if you wish to have the heating on without the hot water the connection from terminal 1 of the programmer will need to be added.
Thanks once agaon - this is hugely helpful.
I removed the timer and jumped the wires between L, 3 and 4 as indicated and hey presto, everything works. If I up the room stat, the 3 port valve works and the rads warm up. If I up the cyl stat, the boiler also fires and heats the water in the tank.
I.e the stats work, the boiler works, the 3 port valve works - everything works as indicated it should (obviously we can't test the CH only function in the above hard wired condition).
So, as I understand it - my timer is knackered (knowing the contacts are solid and surgically cleaned and prepped).
I'll order a new timer tonight - any other suggestions other than that Draytom LP522?
This then leaves me with the issue of no connection to terminal 1 and the likely(?) cause of the no CH only functionality?
I do have a multi-meter, but can't think past having 60 foot long leads with one in the kitchen cupboard and the other upstairs in the airing cupboard trying to find a continuity beep to establish which end is which so I know what can and can't be connected to T1. Or is there an easier way to do this?