I understood that the maximum length of a cable on a 2.5mm2 32amp ring was 73m, not 106m.
I would certainly go for two rings rather than one.
Also, traditionally at least, the floor area served by a ring should not exceed 100m2 - though this does seem pointless now bearing in mind things like electric heaters are not used in the way they were decades ago.
I was given the 106 meter length at an IET lecture, I also could not get the results, so next lecture I asked the question, and I was told for volt drop on a ring final we assume 20 amp drawn from centre point and the rest even distributed, so average for rest is 6A on a 32A MCB so we calculate design current as 26 amp when working out volt drop. With that then you do get 106 meters.
The problem is with radial we use same idea, 20A at furthest point with rest even distributed, which since likely the MCB is 20A means 32 meters on a radial that goes to 42 meters with a 16A radial.
Now next question is with two rings how to split? Splitting side to side of house reduces cable used compared with up/down so on a technical footing it is better, also since upstairs likely less current is used than down stairs likely load more equal between the two rings. However traditionally we go up/down so that is what people expect and to move from it could mean wrong MCB is switched off.
However a MCB does not isolate it does not switch neutral, and one should test for dead, so not realising the socket is not dead is the fault of person working on it.
I found calculating volt drop with Correction factor Ct is not easy, so years ago I wrote a Excel program, however when my phone stopped doing free Excel I moved to Java Script. I still use it today.
My thoughts were if I do a EICR and miss a volt drop issue, could it come back and bite me latter? One can calculate volt drop from the loop impedance, so some one can with relative ease check. However once you factor in reading errors then not so easy to show some one got it wrong.
So 0.35 loop impedance at consumer unit and 0.94 (line - neutral) at furtherest point and that shows 106 meters, but 0.34 and 0.95 and you have exceeded volt drop by 0.5 volt, reverse 0.36 and 0.93 and your under by 0.5 volt. So at best readings are +/- 0.5 volt. Now add to this the designed does not need to use 20 amp centre and 12 even spread, he could decide on 16 amp centre and 16 even spread so could work it out as 24 amp design current, that gives him an extra volt to play with.
So in real terms one has to allow for 2 volt over before one could be sure there was a design fault. So the installer would need to go over by 30 meters before one could be 100% there was an error and you would need to measure cold. So by time you take into account the circuit may not be cold before you could say without fear of being wrong that too much cable has been used, it would have to calculate as an extra 50 meters.
So over 1 ohm line - neutral impedance I would be making a comment, under that would not say anything unless asked. Hind sight should have used PSCC not impedance, but only use the program for comments of forums now so not worth rewriting. And when I look at the forms, it does not ask for line - neutral PSCC or loop impedance to be entered measured at furthest point. So one could hardly prove it was incorrect last time a EICR was done. It is possible some one has extended the circuit.
So does excessive volt drop matter? Well for refrigeration equipment yes, and for TV's Radio's and like before the switch mode power supply. But volt drop is becoming less and less important. I have seen on caravan sites where battery chargers have failed due to volt drop, and I well remember a shrink wrap machine failing due to volt drop.
Fluorescent fittings have failed after 20 years of use due to volt drop, however that is because the DNO have reduced the voltage to cater for solar panels, not house internal wiring, in March 1993 we had an extra 9 volt volt drop added to UK supply, there were auto transformers sold which would auto change tapping to maintain a steady voltage, however they stopped working when there was high demand, so most regarded them as snake oil.
It would be interesting to hear how many actually measure the volt drop with an EICR, I would guess around 2%?