Line - earth needs to be 1.37Ω which at 230 volt = 167 amps using ohms law. To ensure a type B 32A MCB will trip.
Line - neutral needs to be 0.94Ω (assuming incomer at 0.35Ω) which at 230 volt = 244 amps using ohms law. To keep volt drop to 5%.
I have said before I can't think of a case where excessive volt drop would be dangerous. With say a fan heater the fan could stop and as a result it could over heat but for the fan to stop the volt drop would have to be huge and the thermal fuse would blow anyway. Yes it could damage refrigeration equipment where the old overload is used, but modern inverter units would not be effected unless a massive drop.
As to line - earth using even an EZ150 Martindale tester should ensure it is safe. OK it shows fault at 1.5Ω rather than 1.37Ω but only at centre of the ring would the trip not trip with a fault so if the Martindale tester shows OK on all sockets then in real terms only the centre sockets could have a problem and the RCD would likely trip anyway.
Why the Martindale EZ150 has the first light at 1.5Ω I don't know. But the price jumps from £50 to £250 if you want to use a proper loop impedance tester however for a full re-wire I think one should use a proper loop impedance tester. The same goes for the RCD tester, in my house where I know the RCD does work due to it tripping from time to time I still don't know if it trips within the 40 milliseconds without a proper tester.
But where one pays the LABC to be responsible for site safety then I would say you can reasonably expect them to test using a loop impedance tester and with a RCD tester to verify your readings. How many tests are done I suppose would depend on how happy the inspector is with your work. I suspect the LABC inspector is lazy and only tests one or two sockets, but at the end of the day should the DIY guy get it very wrong and as a result kill some one, it would be the LABC inspector who would be in court as the DIY guy has paid him a lot of money to do that inspection.
So in real terms getting it wrong could mean the circuit will fail inspection. However from what has been said that's very unlikely. Yes the LABC inspector who was responsible for my dad's house never set foot in the house after I had completed the work, likely seeing we did have the meters he was sure I would have done a good job, and since I do have the exams under my belt I could have not really have told a court I thought it was OK if it was not, the exams show I have the skill.
But assuming the DIY guy has not passed exams to show he knows what he is doing then the LABC inspector would have to visit or risk a court appearance should something go wrong.
Line - neutral needs to be 0.94Ω (assuming incomer at 0.35Ω) which at 230 volt = 244 amps using ohms law. To keep volt drop to 5%.
I have said before I can't think of a case where excessive volt drop would be dangerous. With say a fan heater the fan could stop and as a result it could over heat but for the fan to stop the volt drop would have to be huge and the thermal fuse would blow anyway. Yes it could damage refrigeration equipment where the old overload is used, but modern inverter units would not be effected unless a massive drop.
As to line - earth using even an EZ150 Martindale tester should ensure it is safe. OK it shows fault at 1.5Ω rather than 1.37Ω but only at centre of the ring would the trip not trip with a fault so if the Martindale tester shows OK on all sockets then in real terms only the centre sockets could have a problem and the RCD would likely trip anyway.
Why the Martindale EZ150 has the first light at 1.5Ω I don't know. But the price jumps from £50 to £250 if you want to use a proper loop impedance tester however for a full re-wire I think one should use a proper loop impedance tester. The same goes for the RCD tester, in my house where I know the RCD does work due to it tripping from time to time I still don't know if it trips within the 40 milliseconds without a proper tester.
But where one pays the LABC to be responsible for site safety then I would say you can reasonably expect them to test using a loop impedance tester and with a RCD tester to verify your readings. How many tests are done I suppose would depend on how happy the inspector is with your work. I suspect the LABC inspector is lazy and only tests one or two sockets, but at the end of the day should the DIY guy get it very wrong and as a result kill some one, it would be the LABC inspector who would be in court as the DIY guy has paid him a lot of money to do that inspection.
So in real terms getting it wrong could mean the circuit will fail inspection. However from what has been said that's very unlikely. Yes the LABC inspector who was responsible for my dad's house never set foot in the house after I had completed the work, likely seeing we did have the meters he was sure I would have done a good job, and since I do have the exams under my belt I could have not really have told a court I thought it was OK if it was not, the exams show I have the skill.
But assuming the DIY guy has not passed exams to show he knows what he is doing then the LABC inspector would have to visit or risk a court appearance should something go wrong.