Also, the cable might not be spot-on 2.5mm² and, as it could cope with 54A at the centre, it isn't going to reach 70° in normal usage.
Right, at last I think I am starting to understand ...Yes but they are all around 0.004. Certainly a lot higher than 0.0017 (for 0.923 Ct)
Quite so. I was going to go on to explain all the 'problems' I am having with that equation, and you highlight some of those there.I don't understand why this equation is for ≥30°. It cannot also be correct for ambient temperatures higher than that, surely. .... If it is correct for 30°, would it not work for any ambient temperature selected? ... If so, why not just put the symbol Ca in the equation?
Not really. As I said, what you have been doing is calculating the VD at 70°, without any consideration of Ib and It (or Iz), so that will usually go beyond a 'worst case' ('in normal service' - i.e. when teh circuit is not being used beyond its design parameters). The implication of the tabulated CCCs is that a conductor carrying the indicated current will (with the installation method concerned) reach a temp of 70. If me assume Method C 2.5mm cable, the 'worst case' being considered in 'the Example' would be for a cable with a CCC of 27A to be carrying 13A - and that would clearly result in a ('worst case') conductor temperature of considerably less than 70°. Even if the entire 13A load were at the centre, each leg (with a CCC f 27A) would only be carrying 16A.Anyway, the thread has been trying to work out the maximum ring length, so, as is usual, the worst case scenario has been used.
I don't understand what you mean by "the usual 20 to 70". Whilst tp (=70) comes into the equation, as above, ambient temp does not. In terms of the parameters which exist in their equation, the 0.923 figure is correct.Also, how does this come to 0.923 when they are using the usual 20 to 70°?
Yes, the 20 is It - ie. they are talking about a 'just-compliant' ring final with a CCC of 20A.Ah. I may have confused the 20 as 20° ...
Yes, but as I have explained, although one has to put the maximum conductor temp, tp (=70°) into that equation, since Ib is less than It, it is trying to work out what conductor temp would actually be obtained - and, since that would be less than 70°, results in a calculated Ca less than 1, indicating that the VD would be less (with that Ib and It) than it would be if the cable were 'fully loaded' (Ib=It), and hence assumed to reach 70°.... but I don't think that makes any difference to my question. The top line is using 18 which relates to 70°, but then it says to calculate Ct and get 0.923, they also quote 70°.
I perhaps should have added that, per my penultimate post, the way in which that is being 'realised' by Equation 6 seems all wrong to me.Put another, perhaps simpler, way - the tabulated values of mV/A/m relate to a cable loaded to its maximum tabulated CCC, and achieving 70° as a result. With any load less than that maximum tabulated CCC, the temp will be lower, hence the mV/A/m less than the value tabulated (which assumes 'fully loaded', hence 70°).
Indeed, but also, in the (I would imagine very common) situation in which CCC is 27A, rather than 20A, Ct then becomes 0.898 and (accepting what I believe to be potential shortcomings of the calculation) the maximum length thereby rises to 109.5 metres - conceivably of some interest to those re-wiring castlesYes, not much point calculating that a 2.5mm² ring can be 106m (or 108.7) long for the actual loading if part of it later has to be increased to 4mm².
Right - scribbling done. I actually make it about 104.3 metres. As I said, it's not a trivial calculation - so are you sitting comfortably .....
I will assume that the "12A evenly distributed along the two legs" is equivalent to 6A at the middle of each leg (i.e. a quarter of the total ring length from the CU).
Of that 6A, 4.5A will travel by the 'short route' and 1.5A by the 'long route'. The two 1.5A 'long route' currents (one from each side of the ring) travelling in the two 'middle quarters' of the ring will cancel, since they are going in opposite directions, and therefore will have no effect on VD.
Considering just 'one side' of the ring, the current in the half of that leg (i.e. quarter of the ring) more remote from the CU will just carry 10A (half of the 20A load at the centre of ring) (the two 1.5A 'long route' currents having cancelled). The current in the half of the leg closer to the CU will carry 14.5A (10A from central load, plus 4.5A of the 6A load on this leg, plus 1.5A of the 6A load on the other leg).
Yes, I actually "picked it up" myself, in post #44 ...I haven't read the whole thread so I don't know if anyone else has picked this up.
No-one has jumped on me yet, (despite the passage of best part of 24 hours), but I've just spotted the flaw myself!
There was clearly a fundamental flaw - since, with my calculations, whilst there was clearly a total of 32A worth of loads, there was only 29A coming out of the CU!
Whilst I still think I was correct in saying that the two 1.5A currents ('taking the long route') would 'cancel' in the two 'middle quarters' of the ring (so each just carried a net 10A - half of the central load), what I had overlooked was the fact that the same is not true in the two 'outer' quarters (the ones connected to the CU), since each of them carries the 1.5A 'long route' current from the other side of the ring. The current in those two 'outer quarters' is therefore (as I should have realised it had to be!) 10 + 4.5 + 1.5 = 16A - i.e. half of the 'central 20A load' plus 4.5A of the 'short route' 6A load on 'this' side plus 1.5A of the long route' 6A from the other side. My final expression therefore should have been ...
L = (11.5 x 4) / (26 x 0.018) = 98.3 metres
... which, of course, is exactly what 'the book' (and others) say (but I still don't know where BAS's 24A came from), and it is the temperature correction of that which takes it up to around 106 metres ('around', since it depends upon exactly which correction factor one chooses!).
Apologies for the confusion.
Well done, simple mistake like that are so easy to miss when they cancel elsewhere.Yes, I actually "picked it up" myself, in post #44 ...
Kind Regards, John
Quite - I am certainly as fallable as anyone else, probably more. It took me 24 hours to detect my 'flaw', which became obvious when I noticed that with my (erroneously calculated) figures, there was a total load of 32A but only 29A coming out of the CUWell done, simple mistake like that are so easy to miss when they cancel elsewhere.
Indeed. The former is, of course, the 'worst case', but it appears that the OSG accepts an assumption of 20A at the centre point and the remaining 12A evenly distributed.All seems to refer to the load being evenly distributed or at the centre point.
I'm not sure that's a 'spanner in the works' - you're simply moving away from the assumptions on which one should undertake the calculations. The closer the total load gets to one end of the ring, the longer could that ring be (VD-wise). As it approached the end of the ring (although cable would then be overloaded), the permissible ring length would approach infinity! What we have to do is design of the basis either of the worst case (all load at centre) or some reasonable assumption of likely use (such as the OSG's 20A at centre plus 12A evenly distributed).I'll put a spanner in the works now and assume all the load is at one point such that there is 27A in one leg and 5A in the other with a VD of 11V, so in very round terms (Head not calculator) 11/27=0.4Ω and 11/5=2Ω, total 2.4Ω. 2.4/0.015=160m.