Find one who knows what he is doing.Not according to the 3 sparks I've had in.
That would seem to be pointless.I can double check with them.
That's 12kW which at 240V is 50A.9kw hob, and 3kw oven.
With cooking appliances, what we call diversity is applied.
That is the first 10A and 30% of the remainder.
So 10A plus 30% 0f 40A is 10A + 12A = 22A.
4mm² T&E has a current carrying capacity of 37A (as long as it is not run through thermal insulation).
So the 32A breaker and 4mm² cable is fine.
Despite this people tend to still (for historical reasons) use 6mm² cable. Are you/they sure it is 4mm²?