Has he ever heard of a 'cooker'? An oven and hob in one and what the label on the circuit breaker states.
Well, the ratings will be quoted at 240V, at 230V the Wattage will be less - but that doesn't make much difference.
As I have shown you, the design current of the circuit is 22A.
I don't blame you for being wary but the system has been in use for decades - and works.
35 is more than 22 so fine.
You could get a new - or probably better would be an older - electrician.
10mm² is used for the supply cable to many premises to supply everything; cooker, heating, shower, everything; as they (and you might) only have a 60A main fuse.
I wonder how that works.
Thank you again. Honestly yes I think getting another electrician in is probably the best approach. Considering not one of the ones I had in already even thought to pop off the cover of the oven isolator to see what the existing supply cable is.
Thanks again, have a good evening.