The family are thinking of either selling or letting the property out, which I presume would require a EICR cert.
Ok, first the basic's of how EICRs work.
An EICR compares the wiring in the property to *current* electrical safey standards, any deficiencies are then supposed to be given a code.
C1 - Immediately dangerous (roughly, you can touch live parts)
C2 - Potentially dangerous (roughly, something that falls significantly short of current safety standards but something else would have to go wrong for that danger to actually manifest)
C3 - Improvement reccomended (relatively minor issues)
FI - Further investigation, the inspector found an issue but was not able to determine which code is appropriate within the time/resources/access.
There are no hard and fast rules on what code to give each deficiency. However there *is* industry guidance and IMO it would be a foolhardy inspector who coded significantly more leniantly than the industry guidance.
The EICR as a whole is either "satisfactory" or "unsatisfactory". A satisfactory EICR can have C3s, but it cannot have C1, C2 or FI.
My question is then that will require a new consumer unit ? Previous one doesn't have RCD or RCBO.
Under industry guidance, lack of RCD protection for a circuit can be either a C2 or a C3 depending on the specifics of the circuit.
If you have no RCD protection at all then that is likely to attract at least one C2. It is possible that a "spot fix" could be applied to only the circuits with C2s, but it is generally considered more sensible to replace the CU and clear up the C3s at the same time.
Kitchen and 1 bedroom has had downlight installed a 5 years ago by sparky. But based in what I've read recently, this will now fail the EICR? Is this correct?
Shouldn't do if they were installed competently and suitable for the environment they are installed in.
In general, EICRs don't care when work was done.
Also to have consumer unit UPGRADE with RCD would it a require a Full rewire?? Or can it be done without a rewire ?
If the wiring was correctly installed and is still in good condition there is no reason it cannot continue to be used.
I had a new consumer unit fitted and no rewire necessary. The downlights in the bathroom had to be replaced for a reason I forget
My understanding is that if a light is in the "bathroom zones" than it requires at least an IPx4 rating. If not in the zones then there are no specific requirements, but there is the catch all that "equipment must be suitable for it's environment". That leaves a lot of room open for judgement on the part of the inspector.