Yes, but if they all use the same methods of testing with the same inputs to achieve the same parameter levels it would mean that they are all the same.
It would (and does) mean that the configurations of their products tested by various manufacturers would all
at least satisfy the minimum requirements specified by the relevant Standard(s). However, that does not necessarily preclude the possibility of different products exceeding the minimum requirements by varying amounts (which you might interpret as meaning that some our 'better' than others ....
If not - and some were better than others, I am sure they would advertise the fact. "Buy ours - tested to 50% in excess of the required standard."
With the sort of mass-market products we are talking about, I doubt that it often works like that. I think it is more likely that they usually just test 'per the minimum requirement' and regard the answer as 'yes/no', and claim no more than that the product satisfies the (minimum requirements of the) Standard. In other words, if a Standard required, say, a maximum temperature rise of X degrees when a current of I amps flows for T hours (plus any other 'conditions'), I suspect that many will just test with I amps for T hours and confirm that the temp rise under those conditions is no greater than X, and will not examine the effect of increasing I and/or T or comment on the fact that the temp rise they saw (with I and T) was actually a lot less than X. If they unilaterally imposed tests which were more 'demanding' than the minimum requirement of the Standard(s), they would probably find themself having to throw out batches which were actually Standard-compliant.
However, that's a bit of an aside, and is not really the point. The point (in relation to type-tested CUs etc.) is that, regardless of what 'pass' criteria for tests they utilise, their tests are based on specific configurations of their product, using combinations of components/devices that they 'approve' (invariably only ones of their own manufacture), and hence that type testing only applies to the tested combinations/configurations.
Hence, MK may 'type test' a CU using various combinations/configurations of MK devices within it, and confirm that all those combinations/configurations pass the required tests - hence 'type tested'. However, if someone comes along and, say, substitutes a Wylex or Hager device (if they will fit) for one of the MK ones, then stillp (and 'the establishment' as a whole) will argue that that may change things in some way (e.g. by adjacent MK and 'other' devices interfering with one another in some way), such that the unit would not pass the required tests (if tests were undertaken on such a configuration). Hence, if MK have not tested configurations with Wylex/Hager devices in it, they cannot 'be sure' that such a unit would pass the tests - hence not 'type tested'.
Very little is impossible, so one cannot really argue with strict view of 'the establishment' - but you, I and others may have views as to how likely it is that installing an 'alien' device (which will fit mechanically), or bolting the incoming L to the busbar will have a detrimental effect on the safety of the unit.
It is also rather "interesting" that the requirement for a type-tested CU ceases to apply if the supply is not single-phase. I presume it's not intended to make sense!
I wonder how many electricians have
never done something which theoretically invalidates the type-testing of a CU?
Kind Regards, John