Therefore, is it just related to getting electric shocks when operating a switch?
I assume it is nothing to do with working inside.
I assume it is nothing to do with working inside.
In that case, I'm a bit confused. If that is the case, why does BS7671 appear to single out single-phase supplies ≤100A under the control of ordinary people for its requirement for a "CU" (type-tested DB)?All the Parts of IEC (and BS EN) 61439 include requirements for type testing.
The distinction between ordinary and skilled/instructed? It's more general than that. Many standards requires that access inside equipment is restricted to persons having suitable training/experience/supervision.Therefore, is it just related to getting electric shocks when operating a switch?
I assume it is nothing to do with working inside.
It's not just a type-tested DB, it's a type-tested DB intended for use by ordinary persons.In that case, I'm a bit confused. If that is the case, why does BS7671 appear to single out single-phase supplies ≤100A under the control of ordinary people for its requirement for a "CU" (type-tested DB)?
Kind Regards, John
I've always been a bit confused by that. It seems to be referring to those who 'use', not design, install or maintain, the DBs - and it's difficult to see how such a user, no matter how much training, experience and understanding they may have, can do much about the hazards that are claimed to exist if the DB they are 'using' has been so configured, modified or installed that it does not qualify as "CU". Can you perhaps explain/clarify?"Skilled or instructed persons" are considered to have training and experience such that they understand the risks associated with the use of electricity, and can take whatever measures are necessary to avoid those risks. "Ordinary persons" do not have that training/experience and therefore need to be protected.
I think you're conflating two sources of your confusion! Consider for example that someone modifies a CU in such a way that the busbar shrouds cannot be fitted. An ordinary person might not recognise the increased risk of electric shock but a trained person would.I've always been a bit confused by that. It seems to be referring to those who 'use', not design, install or maintain, the DBs - and it's difficult to see how such a user, no matter how much training, experience and understanding they may have, can do much about the hazards that are claimed to exist if the DB they are 'using' has been so configured, modified or installed that it does not qualify as "CU". Can you perhaps explain/clarify?
Kind Regards, John
This is confusing!It's not just a type-tested DB, it's a type-tested DB intended for use by ordinary persons.
andBS7671 530.3.4 said:For an installation with a 230 V single phase supply rated up to 100 A which is under the control of ordinary persons, switchgear and controlgear assemblies shall either comply with BS EN 61439-3 and Regulation 432.1 [device breaking capacity] or be a consumer unit incorporating components and protective devices specified by the manufacturer complying with BS61439-3, including the conditional short-circuit test described in Annex ZB of the standard.
The BS7671 definition of a consumer unit says nothing about it being intended for use by ordinary persons (only "principally in domestic premises"), whereas 530.3.4 says that if the installation is under the control of ordinary persons (plus the other conditions) one way of satisfying the regulation is then for the "switchgear and control gear assemblies" to consist of a consumer unit. Can you help me to understand what this all means. I thought I understood, but you are making me wonder!BS7671 Part 2 (Definitions) said:Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.
All product standards require type testing, which is the testing of a (usually small) number of samples to verify that the requirements of that standard are met. This is distinct from routine testing, which is testing of every product manufactured to ensure that some of the requirements are met - typically for electrical products this would include some form of insulation test. Then there is sample testing, in which a proportion of production is removed and tested more intensively than for routine testing.What I'm trying to determine as I've never been sure what "type testing" is.
I had presumed it relates to the product behaving itself in normal use - i.e. not melting or catching fire.
Indeed - but I thought that the people who were required to be "skilled or instructed" were those 'in control of" the installation (i.e., I thought, 'users'), not designers, installers or maintainers, and, taking your example, I don't see that such a 'user' would necessarily even know about the modification of the CU/DB.I think you're conflating two sources of your confusion! Consider for example that someone modifies a CU in such a way that the busbar shrouds cannot be fitted. An ordinary person might not recognise the increased risk of electric shock but a trained person would. It seems self-evident that ordinary persons are not responsible for the design or maintenance of DBs of any sort.
BS 7671 requires that consumer units conform to BS EN 61439-3, which is titled "Part 3: Distribution boards intended to be operated by ordinary persons (DBO)"The BS7671 definition of a consumer unit says nothing about it being intended for use by ordinary persons (only "principally in domestic premises"), whereas 530.3.4 says that if the installation is under the control of ordinary persons (plus the other conditions) one way of satisfying the regulation is then for the "switchgear and control gear assemblies" to consist of a consumer unit. Can you help me to understand what this all means.
If the DB (or any other part of the installation) can be modified without their knowledge, then they cannot be said to be "in control" of the installation.I thought that the people who were required to be "skilled or instructed" were those 'in control of" the installation (i.e., I thought, 'users'), not designers, installers or maintainers, and, taking your example, I don't see that such a 'user' would necessarily even know about the modification of the CU/DB.
Sorry, I missed this one amongst the flurry of much longer posts!I hope in that case that your distribution boards contain 16kA devices ..
Not really, I'm afraid. In fact it merely illustrates the reason for my confusion. As I read it, 530.3.4 is saying that (in the type of installations described at the start) switchgear & controlgear can EITHER consist of a "Consumer Unit" (which you say above is what 61439-3 relates to) OR must comply with 61439-3 (and reg 432.1) - which appears to be the same Standard!BS 7671 requires that consumer units conform to BS EN 61439-3, which is titled "Part 3: Distribution boards intended to be operated by ordinary persons (DBO)" An assembly cannot be said to conform to that standard unless it meets all the requirements of the standard, including the type-testing. Does that help?
The distinction between ordinary and skilled/instructed? It's more general than that. Many standards requires that access inside equipment is restricted to persons having suitable training/experience/supervision.
Are those two statements not incongruous?Consider for example that someone modifies a CU in such a way that the busbar shrouds cannot be fitted. An ordinary person might not recognise the increased risk of electric shock but a trained person would.