Fitting consumer unit vertically

.. OR that it must be a "Consumer Unit" (also complying with 61439-3). That seems to imply that, if one adopts the first approach (the 'either' ratherthan the 'or'), that one's DB/CU does not necessarily have to satisfy all of the BS7671 definition of a CU, even though it has to comply with 61439 (and 432.1). Is that correct?
I did write "if you are not using a CU you must ensure that your DB conforms to 61439-3 and meets 432.1".
I don't understand what you are asking. A CU has to meet the requirements of the standard for DBOs (61439-3). If used in a BS7671 installation, it must meet the requirements of BS7671, one of which is that it must conform to 61439-3.


again, I ask you whether the breaking capacity required by the Standard is so high that they/you are sure that it will be higher than the PFC in any installation, thereby satisfying 432.1 of BS7671?
And again, I point out that the standard for CUs is for distribution boards for use by ordinary persons, which will include all domestic installations.
 
Sponsored Links
I did write "if you are not using a CU you must ensure that your DB conforms to 61439-3 and meets 432.1".
You did, but it appears that if (in the scenario described in 530.3.4, including a reference to 'ordinary persons') one IS using it CU, it also needs to conform to 61439-3, and would also need to satisfy 432.1 (which appears to apply to any installation which has combined fault/overload protection devices, regardless who is 'in control' of it). So ......
I don't understand what you are asking.
I'm essentially asking what is the difference between the 'either' and the 'or' of BS7671's 530.3.4.
And again, I point out that the standard for CUs is for distribution boards for use by ordinary persons, which will include all domestic installations.
Yes - but, as above, 432.1 requires that the devices be able to be able to break the PFC of the particular installation. I don't really understand how the Standard can guarantee that the breaking capacity it requires will inevitably be at least as high as the PFC of any installation - unless, as I have suggested, the breaking capacity required by the Standard is so high that it's next-to impossible that any installation would have a PFC higher than that figure.

Kind Regards, John
 
Sponsored Links
if one IS using it CU, it also needs to conform to 61439-3
If one is using a CU, then by definition it will conform to BS EN 61439-3. If it doesn't then it isn't a CU.
I'm essentially asking what is the difference between the 'either' and the 'or' of BS7671's 530.3.4.
Ah, I see (I think). Either the assembly shall have an adequate prospective fault current withstand, or it shall withstand 16 kA.
What I think it is trying to say is that if the PFC is greater than 16 kA, then 432.1 applies, i.e. the designer shall ensure that the protective device(s) can withstand whatever that PFC might be. OTOH they might be saying that 16 kA is deemed to be adequate for all installations <100A at 230V single-phase under the control of ordinary persons.

If you're that concerned, put in a comment on the DPC.
 
If one is using a CU, then by definition it will conform to BS EN 61439-3. If it doesn't then it isn't a CU.
I don't think it's necessarily that simple in the eyes of 7671. The 7671 definition of a CU does not mention any Standards, so presumably something could satisfy that definition, per se, without having to comply with any Standards, 61439-3 or otherwise.

However, the reg we are discussing (530.3.4) goes beyond talking just about a "Consumer Unit". For the installations that regulation relates to (single-phase, ≤100A and under the control of ordinary persons), one way of satisfying the reg is not to just have "a CU" (presumably per the 7671 definition) but, rather a CU "incorporating components and protective devices .... complying with BS EN 61439-3" (something not mentioned in the 7671 definition of a CU).
Ah, I see (I think). Either the assembly shall have an adequate prospective fault current withstand, or it shall withstand 16 kA.
I remain confused. Whichever of the 'either/or' (of 530.3.4) one chooses to use, the reg has a requirement that the devices conform to 61439-3, which you say specifies a 16kA breaking capability. That would mean that nearly all domestic installations would have to have 16kA (or higher) devices - something that I didn't think was the case (and seemingly similar with BAS, judging by his recent comment). As you go on to say, that would mean that 432.1 would only become relevant if the PFC were greater than 16kA - which I find rather hard to believe would ever be the case with the sort of installation that reg is talking about. As I've said before, although my experience is extremely limited, I don't think I've ever actually seen a PFC above (or significantly above) 1kA, let alone 16kA.
OTOH they might be saying that 16 kA is deemed to be adequate for all installations <100A at 230V single-phase under the control of ordinary persons.
Maybe, but if that's what they are "trying to say", I don't think thet have been very successful. Furthermore, as above, I didn't think that such installations did need 16kA devices.
If you're that concerned, put in a comment on the DPC.
I might, but I don't really like making comments unless I have something constructive to suggest as a 'change' - and since I haven't got much of a clue as to what they are trying to say, I wouldn't really know what to suggest!

In terms of my personal installation, I have a fairly simple question (but the answer may not be simple!), and it's one that does not depend upon who is 'in control' of my installation. 530.3.4 does not apply to my installation, regardless of who is 'in control' of it, since it does not have a single-phase supply. Similarly, 432.1 (which doesn't mention anything about who is 'in control) does not apply, either, because my (TT) installation does not use the same devices for fault an overload protection.

Since neither of those regs apply to my installation, my 'simple question' is ... what are the requirements in relation to CUs/DBs in my installation, both in general and in relation to the breaking capacity of my devices??

Kind Regards, John
 
Would it be possible that each of your CUs is an installation, by the definition, and so has a single phase supply?
 
Would it be possible that each of your CUs is an installation, by the definition, and so has a single phase supply?
You tell me - although I wouldn't have thought so. The definition is almost laughable, and certainly not helpful:
BS7671 said:
Installation (see Electrical installation)

Electrical installation (abbr: Installation). An assembly of associated electrical equipment having co-ordinated characteristics to fulfill specific purposes.
:)

Kind Regards, John
 
I don't think it's necessarily that simple in the eyes of 7671. The 7671 definition of a CU does not mention any Standards
Part 2 defines it as "A particular type of distribution board comprising a type tested coordinated assembly for the control and distribution of electrical energy, principally in domestic premises...".

530.3.4 says

"For an installation with a 230 V single-phase supply rated up to 100 A that is under the control of ordinary persons, switchgear and controlgear assemblies shall either comply with BS EN 60439-3 and Regulation 432.1 or be a consumer unit incorporating components and protective devices specified by the manufacturer complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3."​

Do you really want to argue that when BS 7671 references a consumer unit it does not mean a type tested assembly complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3?


so presumably something could satisfy that definition, per se, without having to comply with any Standards, 61439-3 or otherwise.
If 530.3.4 applies, then either method of complying requires that the DB/CU complies with BS EN 60439-3

For the installations that regulation relates to (single-phase, ≤100A and under the control of ordinary persons), one way of satisfying the reg is not to just have "a CU" (presumably per the 7671 definition) but, rather a CU "incorporating components and protective devices .... complying with BS EN 61439-3"
Shall I be generous and assume that you missed "including the conditional short-circuit test described in Annex ZA of BS EN 60439-3" by accident?

That "incorporating components and protective devices specified by the manufacturer complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3" is what makes a BS EN 61439-3 DB a CU.


(something not mentioned in the 7671 definition of a CU).
See above - do you really want to argue that when BS 7671 references a consumer unit it does not mean a type tested assembly complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3?



I remain confused. Whichever of the 'either/or' (of 530.3.4) one chooses to use, the reg has a requirement that the devices conform to 61439-3, which you say specifies a 16kA breaking capability.
I believe that the "conditional short-circuit test described in Annex ZA of BS EN 60439-3" relaxes that capability requirement. Basically, if you have a type tested coordinated assembly incorporating components and protective devices specified by the manufacturer complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3, in an installation rated at no higher than 100A the devices do not have to be 16kA ones.



That would mean that nearly all domestic installations would have to have 16kA (or higher) devices - something that I didn't think was the case (and seemingly similar with BAS, judging by his recent comment).
My recent comment was prompted by you saying that you don't have to worry about what 530.3.4 says about type tested CUs.


As you go on to say, that would mean that 432.1 would only become relevant if the PFC were greater than 16kA - which I find rather hard to believe would ever be the case with the sort of installation that reg is talking about. As I've said before, although my experience is extremely limited, I don't think I've ever actually seen a PFC above (or significantly above) 1kA, let alone 16kA.
Maybe, but if that's what they are "trying to say", I don't think thet have been very successful.
As with Ze, you can either measure the PFC or use the declared figure. AIUI the latter will be 16kA. If you want to use a lower figure you would, IMO, have to show what measures you had put in place to prevent that lower figure becoming incorrect through network changes outwith your control.


I might, but I don't really like making comments unless I have something constructive to suggest as a 'change' - and since I haven't got much of a clue as to what they are trying to say, I wouldn't really know what to suggest!
They are trying to say that you must either use

  • A DB which complies with BS EN 60439-3 and 432.1
or​
  • A type tested consumer unit which complies with BS EN 60439-3 including the conditional short-circuit test described in Annex ZA.

In terms of my personal installation, I have a fairly simple question (but the answer may not be simple!), and it's one that does not depend upon who is 'in control' of my installation. 530.3.4 does not apply to my installation, regardless of who is 'in control' of it, since it does not have a single-phase supply. Similarly, 432.1 (which doesn't mention anything about who is 'in control) does not apply, either, because my (TT) installation does not use the same devices for fault an overload protection.
What devices does it use for fault & overload protection?

Bear in mind when you answer that "fault" means L-N just as much as it means L-E.


Since neither of those regs apply to my installation
I think you'll find that 432.1 does.
 
Do you really want to argue that when BS 7671 references a consumer unit it does not mean a type tested assembly complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3?
When BS7671 references a "Consumer Unit" one has every reason to believe that they referring to the item which they have defined in Part 2 of the Standard. Indeed, if, despite it not being included in their definition, the term "Consumer Unit" implied "incorporating components and protective devices specified by the manufacturer complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3.", there would be no need for them to qualify "Consumer Unit" with a repetition of those words in 530.3.4. If, as I now think is the case, they intended that it was a crucial part of what makes a DB a CU, they really should have included those qualifications in the Part 2 definition.
I believe that the "conditional short-circuit test described in Annex ZA of BS EN 60439-3" relaxes that capability requirement. Basically, if you have a type tested coordinated assembly incorporating components and protective devices specified by the manufacturer complying with BS EN 60439-3, including the conditional short-circuit test described in Annex ZA of BS EN 60439-3, in an installation rated at no higher than 100A the devices do not have to be 16kA ones.
Yes, having done some reading I think you are right, my confusion having resulted from the fact that Stillp had told us that BS EN 60439-3 requires 16kA breaking capability. What he didn't do was mention that "conditional short-circuit test in Annex ZA", and it appears that that test allows the device, per se, to have a breaking capacity less than 16kA, but only if there is an upstream BS88-3 fuse ≤100A - the test being undertaken with a 100A upstream fuse.
My recent comment was prompted by you saying that you don't have to worry about what 530.3.4 says about type tested CUs. .... As with Ze, you can either measure the PFC or use the declared figure. AIUI the latter will be 16kA. If you want to use a lower figure you would, IMO, have to show what measures you had put in place to prevent that lower figure becoming incorrect through network changes outwith your control.
Yes, that appears to be how the 16kA figure comes about. Mind you, assuming that your opinion is correct, and given that no-one could put such measures in place, they might just as well say that the devices have to be able to break the declared PFC.

However, as you imply, the odd thing is that the same issue arises with Ze, but we (and BS7671) seem to ignore that. Particularly with TN, many installations have an actual Ze appreciably lower than the 'declared' figure. However, design and testing of circuits and their protective devices are undertaken on the basis of the actual Zs, a component of which is the actual Ze. I have never heard it suggested that one should design so that protection remains compliant if ("due to network changes beyond one's control") Ze rises to the declared value.
What devices does it use for fault & overload protection? Bear in mind when you answer that "fault" means L-N just as much as it means L-E.
Yes, I confess that I hadn't thought of that, but it makes me wonder what 432.1 is all about. That it requires that protective devices should be capable of breaking the PFC is fair enough, and little more than a statement of the obvious. However, under what circumstances does one have separate devices for protecting against overload and L-N faults?

Kind Regards, John
 
A few points of clarification in relation to my recent post ...

What the current BS7671 refers to as Annex ZA of BS EN 60439-3 has become Annex ZB of that Standard. The 18th ed. DPC reflects that change, but ....

We have been discussing 530.3.4, but that reg is something totally different in 18th DPC ( didn't think they did that!). What we would recognise as "530.3.4" appears as 536.4.201 in the DPC.

The test described in (now) Annex ZB of BS EN 60439-3 is called "16kA conditional short-circuit test" - which might explain why I was confused by what stillp told me. The point is that the test is "conditional" on there being an upstream 100A fuse but, with that fuse in place, the device under test must withstand a 16kA fault current.

The use of a device with a lower breaking capacity than the 'maximum' ('declared') PFC when there is another upstream protective device is actually addressed in 434.5.1 (same in 18th DPC) - and that reg appears to apply to all situations, not just those described in 530.3.4 (to be 536.4.201), and not only in relation to 'type-tested CUs'.

Kind Regards, John
 
My recent comment was prompted by you saying that you don't have to worry about what 530.3.4 says about type tested CUs.
I forgot to say ....

... I can't say that it's of any concern to me, but I don't think it's a simple as you suggest. It's not a question of my "not having to worry" about what that reg says, since, unless we tried (I doubt successfully!) to invoke EFLIs suggestion that I could claim to have three single-phase installations, the fact is that 530.3.4 simply does not apply to my installation (with it's 3-phase 'supply'). That means that I cannot 'enjoy' the option that reg gives to rely on Annex ZA/ZB of 60439-3 with a "type-tested CU", rather than have to comply with 432.1 (i.e. 16kA devices).

In other words, it looks as if your comment may well have been more correct than you realised when you wrote, in that the only way of making my installation strictly compliant would be to fit 16kA devices to all my DBs/CUs (which would quite probably invalidate any 'type-testing', anyway!)! ... in other words, if my installation does qualify for that regulation, I cannot 'opt into' it!

Kind Regards, John
 
..unless we tried (I doubt successfully!) to invoke EFLIs suggestion that I could claim to have three single-phase installations..
I don't see why you couldn't. Or at least I don't see why in your sort of situation one necessarily couldn't.

There's always a potential for complications, but if you have no actual 3-phase use (i.e. no 3P loads), and in your house the phases were used for East Wing, West Wing and Servant's Quarters, then why not regard that as three single-phase installations? What about a small block of flats with one incoming 3P supply split to serve Flat 1, Flat 2 & Flat 3? What if there were 6 flats - 1A, 1B, 2A, 2B, 3A, 3B - surely that would be 6 single-phase installations?


In other words, it looks as if your comment may well have been more correct than you realised when you wrote, in that the only way of making my installation strictly compliant would be to fit 16kA devices to all my DBs/CUs
When I wrote that I knew full well what the significance of not having a type-tested CU was.
 
I don't see why you couldn't. Or at least I don't see why in your sort of situation one necessarily couldn't. There's always a potential for complications, but if you have no actual 3-phase use (i.e. no 3P loads), and in your house the phases were used for East Wing, West Wing and Servant's Quarters, then why not regard that as three single-phase installations?
Yes, that's very much my situation (see **). My actual situation is that one phase serves the ground floor and cellar, the second phase serves the first floor and the third phase serves the second floor and outside stuff (garage, garden etc.). There are lots of CUs - 2 on first phase, 3 on second phase, 2 or third phase, and one little one for genny-only circuits. When we first moved in, an electrician tried to persuade me to have one or two 3-phase sockets in the cellar (my 'workshop') and garage, just in case I ever acquired a need, but I never did that.
[** As a matter of interest, originally, there were indeed 'wings' - a south Wing (Billiards Room) and a North Wing (which was the Servant's Quarters, Kitchen and Nursery). However, both those wings were sold off in 1950, and both (yes, including the 'Biliiards Room!) are now separate 5-bedroomed dwellings - I am therefore 'mid-terraced' as far as officialdom is concerned!]
What about a small block of flats with one incoming 3P supply split to serve Flat 1, Flat 2 & Flat 3? What if there were 6 flats - 1A, 1B, 2A, 2B, 3A, 3B - surely that would be 6 single-phase installations?
Indeed. However, my uncertainty relating to my place as it is currently set up is that there is a single 3-phase meter, and that could well be taken to indicate that it was a single 'installation'. I imagine that I could ask to have it changed to three separate single-phase meters, but I suspect that the supplier would then not only regard it as three single-phase "installations" but also three "services", hence three Standing Charges!
When I wrote that I knew full well what the significance of not having a type-tested CU was.
Fair enough. I thought you were suggesting that I could avoid those issues (other than by claiming that I had 3 single-phase installations) by having "type-tested CUs" (i.e. invoking the 'conditional short-circuit test). As I said, if my installation does not qualify me to 'enjoy' 530.3.4, I don't think that would be the case.

Compliant or not, I really don't have any concerns in relation to the breaking capacity of my devices. The last 40m or so of my supply is in ~16mm² overhead/clipped to wall cables. That alone would limit the PFC to about 2kA if I had an L-N fault on one of my phases, even if the transformer were at the end of that cable run (which is far from the case), and I would certainly notice if they changed those to 120mm² cables :) If I recall correctly, the measured PFC is currently around 0.75kA.

For what it's worth, I think that all (certainly most) of my CUs are probably still "type-tested" (i.e. unmodified), in which case my installation(s) would probably be compliant if I called it "3 installations"!

Kind Regards, John
 