If one is using a CU, then by definition it will conform to BS EN 61439-3. If it doesn't then it isn't a CU.
I don't think it's necessarily that simple in the eyes of 7671. The 7671 definition of a CU does not mention any Standards, so presumably something could satisfy that definition, per se, without having to comply with any Standards, 61439-3 or otherwise.
However, the reg we are discussing (530.3.4) goes beyond talking just about a "Consumer Unit". For the installations that regulation relates to (single-phase, ≤100A and under the control of ordinary persons), one way of satisfying the reg is not to just have "a CU" (presumably per the 7671 definition) but, rather a CU "incorporating components and protective devices .... complying with BS EN 61439-3" (something not mentioned in the 7671 definition of a CU).
Ah, I see (I think). Either the assembly shall have an adequate prospective fault current withstand, or it shall withstand 16 kA.
I remain confused. Whichever of the 'either/or' (of 530.3.4) one chooses to use, the reg has a requirement that the devices conform to 61439-3, which you say specifies a 16kA breaking capability. That would mean that nearly all domestic installations would have to have 16kA (or higher) devices - something that I didn't think was the case (and seemingly similar with BAS, judging by his recent comment). As you go on to say, that would mean that 432.1 would only become relevant if the PFC were greater than 16kA - which I find rather hard to believe would ever be the case with the sort of installation that reg is talking about. As I've said before, although my experience is extremely limited, I don't think I've ever actually seen a PFC above (or significantly above) 1kA, let alone 16kA.
OTOH they might be saying that 16 kA is deemed to be adequate for all installations <100A at 230V single-phase under the control of ordinary persons.
Maybe, but if that's what they are "trying to say", I don't think thet have been very successful. Furthermore, as above, I didn't think that such installations did need 16kA devices.
If you're that concerned, put in a comment on the DPC.
I might, but I don't really like making comments unless I have something constructive to suggest as a 'change' - and since I haven't got much of a clue as to what they are trying to say, I wouldn't really know what to suggest!
In terms of my personal installation, I have a fairly simple question (but the answer may not be simple!), and it's one that does not depend upon who is 'in control' of my installation. 530.3.4 does not apply to my installation, regardless of who is 'in control' of it, since it does not have a single-phase supply. Similarly, 432.1 (which doesn't mention anything about who is 'in control) does not apply, either, because my (TT) installation does not use the same devices for fault an overload protection.
Since neither of those regs apply to my installation, my 'simple question' is ... what are the requirements in relation to CUs/DBs in my installation, both in general and in relation to the breaking capacity of my devices??
Kind Regards, John