Although I'm even far less of a generator expert than you, a few comments/questions....
Kind Regards, John.
OK, Trojan, as best as I can........but like I said, I'm no generator expert. My BLUE
The generator doesn't need 'earthing' - you are providing an earth path back to the generator to be used by the installation. I thought it had to be a seperate earth from the supplied (DNO) - but maybe it doesn't. The earth from the generator is connected to the MET because this is where all of the installation's CPCs / Bonding etc should be connected to......it's not to 'earth' the generator - it's to give the installation a path back to the generator.a) Earthing arrangement - single core connected to MET of installation so TN-S? Should the generator have it's own earthing too?
I have to say that I'm rather struggling to see what problem would be posed by a generator supply that was truly floating relative to true earth (e.g. if a DNO-supplied 'earth' were to 'fail'), but 551.4.3.2.1 of BS7671 (which I quoted recently) seems to very clearly state that a standby generator must not 'rely' ('rely' for what?) on a DNO-supplied TN earth, but should be provided with its own earth. Although I've not seen it (costs money!), I've been led to believe that BS7430 says much the same. However, as I said, I don't really understand why.
b) PFC and Ze. It's a back up generator but considered the source of supply so how do you get around this? It can't run just to test at the changeover panel.Surely you can isolate the main supply and run the generator - then you do the necessary 'live' tests for the generator 'supply'.
I would have thought so, too. However, isn't PFC, in practice, going to be determined/limited by the maximum current the generator can supply? I would have thought that a PFC calculated from Ze would usually be 'unsupplyable', at least for more than a few cycles.
a) Means of earthing - Distributors facility as the generator is earthed via the MET?
No. The generator isn't earthed. The generator is providing an earth to the installation.
I fear that we at risk of the usual seantic confusion! Unless it has it's own earth electrode, it's not 'providing an earth'. However, as you go on to say, the conductor from MET to genny is providing an 'alternative' neutral return path from CPCs; 'earth' does not come into it
You need to treat it as two supply - one supply has the DNO provided earth.......the other has the earth provided from the generator.
As above, in the absence of a local electrode, it's not really an 'earth' - so I wouldn't think one could respond to the 'means of earthing' question with an answer 'generator', could one? If no local electrode was being used, I would have thought the correct/honest answer (in relation to the generator supply) would be 'none', wouldn't it?
b) Main protective conductors - None seem to apply
These should be in place anyway (for the existing installation/supply.)
Indeed - although, as you say, it's hard to see that they would theoretically be required if the genny supply really were truly floating wrt true earth. Whatever, assuming that it's true (in terms of the main installation), I would assume that, for the purpose of 'the form', the answer would be 'present and correct'.
Kind Regards, John.