I just meant that if he was replacing like for like, he might argue that as the previous set-up was OK, and the gas flow hadn't changed, there was no need to check the gas pipe.
But its not an argument. Its his lawful duty to install the appliance safely and to spec. There's no guessing. You test it, it doesn't pass, then it can't be commissioned.
But its not an argument. Its his lawful duty to install the appliance safely and to spec. There's no guessing. You test it, it doesn't pass, then it can't be commissioned.
I don't follow. If not taking into consideration any radiators, where is the heat going?
I'm sure there's a whole range of boiler inputs (and outputs) out there.
Nevertheless, it changes nothing. the boilers running safe. so I'd not loose any sleep over it. If working pressure is lower than 13mbar next service with meter pressure still the same then you can assume there is a restriction building in the gas line.
Although you do lose the ability to simultaineously heat water and the radiators. It will only do one or the other at any point in time, prioritising heating the water until demand is satisfied.
You could explain the benchmark form wasn't completed properly, and there appears to be excessive pressure drop.
I think he should install a pressure tapping point on the gas pipe just before the boiler, and then do a thorough pressure drop test.
Depending on the results, you could look at the options in #115 (there have been a couple of comments).
For background, do you know the output of the previous boiler?
Whether or not it condenses also depends on the rad area. If the rads are too small, in cold weather the water temperature to give adequate heating will be too high for condensation.
I don't think the control-stat setting is that critical, as when the weather is moderately cold the roomstat is satisfied and switches off the boiler before control-stat temperature is reached. Up to that point, flow and return temperatures settle at what is needed to dissipate the boiler output, which could allow condensation. Maybe a bit different with a modulating boiler, but that's how I see it. I have W-plan and the control-stat setting is never reached on CH, only on HW.
How many times do you want it repeating.?
The pipework is either seriously restricted or, more likely, is undersized.
The false figures imply that he either knew it was wrong or did not bother to consider it.
I cannot see post numbers but on page 2 the OP describes the pipe run. Most of it is concealed. It seems likely that the first part is iron . If it is most of the rest will be, at least until it leaves the floor and enters the concealed wall. It exits the wall in 15mm, so it may well be the snr all the way down - the previous demand was about 50% of the current and was probably okay.
Any decent installer would know visually that there is an issue.
The OP needs to decide what he wants out of this and demand accordingly.
is the house pre 1970?
Can the Op Accurately measure the diameter of the iron, and maybe post a photo?
That is the point. I as a heating engineer will take into consideration system configuration whereas a lay person may not.
Another hint- it is a system boiler perhaps?
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local