But has it suddenly dropped, or were the 2 sets of measurements looking at different things, with and without flow?Ignore the DIYers advice, if the gas pressure has suddenly dropped, then there's a reason for it.
But has it suddenly dropped, or were the 2 sets of measurements looking at different things, with and without flow?Ignore the DIYers advice, if the gas pressure has suddenly dropped, then there's a reason for it.
But has it suddenly dropped, or were the 2 sets of measurements looking at different things, with and without flow?
It is potentially bad, depending on the OD. Steel pipe is much thicker walled than copper, so less space for gas to flow.
I am certain that the plumber just connected up the old pipes and didn’t check to see anything else as seemingly it wasn’t an issue in the past. Easy work and payday but he would argue that it would have been more expensive to change the pipe work etc.
The pipe that feeds off the meter must be iron as a weak magnet stuck to it. Is that good or bad? Other than the height clearance why do you think he installed
incorrectly. He will argue he just replaced the boiler in situ.
Does one need to be to make a perfectly sensible post as he made above. What do you think, in your personal opinion, was wrong with what he suggested?
Everything is not a specific answer. Try to be specific please...
I apologise - point one was almost certainly correct , the pipework is undersized . The rest is nonsense
Too early to offer a firm opinion, there is a lot the OP seems so unsure of.
Nope they only have to supply 19mb at ecv losing up to 4mb across meter so can be as low as 15mb at meter outlet without them having to do anything.
As I understand it, pressure after the meter should be 21+/-2mb, so 17mb would be non-compliant and the gas supplier should rectify it.
It was installed 2 years ago, and recently serviced by the plumber that installed it. We don't know who serviced it last year, when the 20mb at meter and boiler were obtained, but it's a fair bet it was the same guy. If the installer failed to meet the 1mb drop reg perhaps he should be pulled up, but unless Gas Safe or somebody hears about it, I don't suppose anything much will happen.
Treating it as a "come across" job, where excessive pressure drop is only NCS, presumably it's OK.
As I understand it, pressure after the meter should be 21+/-2mb, so 17mb would be non-compliant and the gas supplier should rectify it. But if it did fall to 17mb, with pipe drop 20-13.5 = 6.5mb, so something like 11mb at the boiler, the boiler output would be down (unless it has a low-pressure cutout, I wouldn't know)
Exactly, that's the point I was makingt has not “suddenly” dropped, the earlier identical readings were almost certainly fake.
Nope they only have to supply 19mb at ecv losing up to 4mb across meter so can be as low as 15mb at meter outlet without them having to do anything
90% of comments on this thread are either guesswork
100% are guesswork. It needs checking on site to be definitive.
Of course, everyone's submissions via the forum are entirely guesswork