You also need a relatively high test current. I've tried to measure tiny resistances with an expensive bench meter and while it had plenty of resolution due to the large number of digits, it just did not produce stable results.
That's probably theoretically true but, for what its worth, my Fluke 1362 only uses about 4V for low resistance measurements - presumably no more than can/could be achieved by a bench meter or a portable DVM which uses a 9V battery. Furthermore, I would expect that any error in measure very small resistances (due to low current or whatever) are very likely to be in what is usually the 'safe' direction (giving readings which are too high).
Measuring "tiny resistances"
with anything is, of course, very iffy, since by far the most crucial factor is the quality (low resistance) of the contact between the probes and what is being measured.
The bottom line is that to properly test electrical installations you need either a set of installation test meters (low ohms, Insulation resistance, RCD test and loop impedance) or you need a multifunction tester that combines those functions.
I can't disagree with that, although one can do a fair bit with just a decent DVM.
However, to get back in context, if a non-electrician is paying an LABC £££ for 'direct notification' it should be them who are responsible for getting the accurate measurements - since there assumption is that the person doing the work is either not competent or not adequately equipped to do it.
As implied by the second set of figures I've recently posted, perhaps one of the biggest rip-offs seems to happen when the person doing the work is an adequate qualified and equipped electrician who provides and EIC but just isn't a member of a CPS. It appears that the LABC then accept the work, I&T and EIC, but charge £168 for 'something'
Kind Regards, John