You'd also have to watch the adiabatic thermal withstand of the 1mm cpc, don't think thats been mentioned, but that would be the same as on pre-80's 2.5mm² anyway....
I'd certainly note it down on a PIR, and like kai I'd be tending towards a code 2, although admittedly thats laregly just a gut feeling towards the issue and you can probably make arguemnts for overload protection to not be required. Either way, its shoddy design/installation practice, there are reasons for the regulations permitting ommiting of overcurrent protection... to enable a domestic hot water heater to be installed on a 32A breaker using 1.5mm conductors is not one of them!
I'd probably write code 2. followed by questionmark and a note to the qualfifying manager for his thoughts on the matter when he reviews it
I'd certainly note it down on a PIR, and like kai I'd be tending towards a code 2, although admittedly thats laregly just a gut feeling towards the issue and you can probably make arguemnts for overload protection to not be required. Either way, its shoddy design/installation practice, there are reasons for the regulations permitting ommiting of overcurrent protection... to enable a domestic hot water heater to be installed on a 32A breaker using 1.5mm conductors is not one of them!
I'd probably write code 2. followed by questionmark and a note to the qualfifying manager for his thoughts on the matter when he reviews it