It's because the people who wrote the Wiring Regulations consider it safe and acceptable.Is it, can you explain why it is allowed?
It's because the people who wrote the Wiring Regulations consider it safe and acceptable.Is it, can you explain why it is allowed?
Why do you say that?433.3.1, is actually about bus-bar chambers and main switchgear.
So are you saying that the diagrams in Appendix 15 depict arrangements which contravene the Regulations?If you understand the meaning of 434, you will understand that 433.3. will never apply in a domestic setting due to the inherent dangers and costs of overcoming those dangers, as required by 434.2.1 (i) (ii) and (iii)
Where does it say that?Because, 433.3.1, is actually about bus-bar chambers and main switchgear.
So if you found such an arrangement when doing a PIR, how would you code it?So are you saying that the diagrams in Appendix 15 depict arrangements which contravene the Regulations?
Yes.
So if you found T&E in use when doing a PIR, how would you code it?And also T&E cable does not comply with regs, unlesss it has some mysterious qualities only understood by the IET.
So why do you say it?Where does it say that?Because, 433.3.1, is actually about bus-bar chambers and main switchgear.
It doesn't.
Is it normally your practice, when doing PIRs, to ignore things which contravene the Wiring Regulations?I wouldn't code it.
And also T&E cable does not comply with regs, unlesss it has some mysterious qualities only understood by the IET.
That regulation has been included in the regulations for a long time — certainly in the 13th edition which was current when I worked in contracting. I used it for just what Holmslaw says it's for – to connect between busbars and switchfuses.So, holmslaw.
1) The regulations do not say that 433.3.1 is actually about bus-bar chambers and main switchgear, but you claim that it is.
Why?
Interesting discussion. Putting my Devil's Advocate hat back on (since I really don't personally want to appear to be arguing in support of the arrangement BAS proposes)....433.3.1 (ii) applies to any situation where you have to connect to something of higher current rating and it is impractical to provide the correct size conductors or protection. But you must comply with the severe requirements of 434.2.1 (i) (ii) and (iii).