I didn't think much about this when I first read it, but now I have thought, I'm a little confused.That regulation has been included in the regulations for a long time — certainly in the 13th edition which was current when I worked in contracting. I used it for just what Holmslaw says it's for – to connect between busbars and switchfuses. ..... Holmslaw has not said that 433.3.1 applies only to busbar/switchfuse connections, only that that's the usual situation. I agree with that. On reading the initial posts I kept thinking "that applies to busbars"; eventually holmslaw said so in a later post.
Just to clarify .... the discussion has been specifically about 433.3.1(ii) (when I've managed to type it correctly!!). In fact, 433.3.1(i) is just common sense (and hardly needs saying), and 433.3.1(iii) is just acceptance of an inevitability (since the has got to be some cable, no matter how short, at the origin of an installation prior to the installation's first protective device.
433.3.1(ii), in itself, simply says that, in the circumstances described, overcurrent protection can be omitted provided that the conductor is protected against fault current as required by Section 434. I would have thought that any device in place which adequately protected a busbar against fault current would inevitably also afford adequate overload protection, in which case 433.3.1(ii) (alone) would presumably be redundant in relation to a busbar - am I wrong?
Are you perhaps talking about not only invoking 433.3.1(ii) to allow the omission of overload protection for a busbar but also simultaneously invoking 434.2.1 to allow the omission of fault protection as well? If so, I guess that makes sense, and may explain some of the confusion in this thread - which has related to a conductor which, per the regs, appears to require fault protection but not overload protection.
Kind Regards, John.