Then it does not matter if some rads have the valve on the flow and others have it on the return. You still adjust the LS vave to give the correct drop.They are Drayton TRV4 which can go on either end.
Still not properly balanced. It can be a time consuming job to get it right. Did you follow the method in the Wiki? Balancing ProcedureThe rads that were cold are now heating up (so the system was out of balance) but the hall isn't getting above 18deg when it used to get to 21deg easily (I know this because the room stat is in there).
Any idea why?
The graphs are misleading. The vertical axis, labelled "Lift", is actually the pressure in the system, which is determined by pipe sizes and lengths, number and size of rads etc. The fact that your boiler is in the loft and about 16 ft off the ground is irrelevant.Looking at the boiler spec it shows a line for the pump at a maximum of 350mbar lift giving 1000l/hr flow. As our boiler is in the loft it has about a 5m lift. Could this be causing the problem as 350mbar is only 3.5m?
Two things might be worth investigating:
If you boiler output is set low (d.0), the pump should be set to two speed operation. It's explained on page 44 of the installation manual - option d.19.
Check the setting of the auto bypass. It's on page 32, item5.8. Try increasing the pressure slightly. This means they bypass will open so soon.