RCD's would normally be expected to protect cable in respect of fault to earth but you would still need to protect cable for the time it takes the OPD to clear short cct's between line and neutral, line and earth - particularly in areas where there is high PSCC or high PEFC. Have a look at 543.1.1
Firstly, a 'short circuit between line and earth' is surely the same as a 'fault to earth', which should be cleared by an RCD - so that only leaves L-N shorts to consider. You have confused me a bit with the order in which you mentioned the regulations - 543.1.1, which you now mention relates only to protective conductors (hence not relevant to L-N shorts), whereas the very similar 434.5.2, which you mentioned last night, relates to any conductor (hence
is relevant to L-N shorts).
However, you are clearly right in saying that the L and N conductors need adequate protection against over-currents due to L-N shorts, even in TT installations (since PSCC can be very high, even if PEFC is very low), and this is seemingly embraced by 434, which relates to negligible impedance L-E
or L-N faults. In determining whether 434.5.2 is satisfied, one considers the PFC (i.e. the higher or PSCC and PEFC) - which, as above, can be high even in a TT installation.
However, even though the ‘fault protection’ (ADS) considerations are similar with both TN and TT, I still think that it will (for T+E cable >1mm²) usually be easier to satisfy them with TT than with TN - since with TN one has to satisfy 543.1.1 in relation to the CPC as well as satisfying 434.5.2 with respect to L & N conductors - and for T&E >1mm², the csa of the CPC is appreciably less than that of the L & N. When I wrote about TT last night, I forget that L, N and CPC all have the same csa with 1mm² T+E.
I don’t think that this significantly alters anything which anyone has said in this discussion, since comments about omitting overload protection have always (literally or by implication) been qualified by “provided fault protection requirements are satisfied’. However, it’s possible that satisfying those fault protection requirements may be rather more difficult than some people may think, particularly in relation to some of the more extreme scenarios we have considered (and particularly with TN).
Kind Regards, John