I have alerted the moderators and asked this to be moved to a new topic. It doesn't sound right though.Sorry for jumping on this topic but it seemed relevant
Those rad outputs seems very low. Are they definitely the type without fins on the back?
The Vokera 29A produces a max heating output or 24kW (29kW for hot water). The spec does not state what the minimum output is but I have calculated it as about 6kw from the gas rate data.
This means that, even when the boiler is running at minimum output, it is producing much more heat than your radiator need - about 60% too much!
This means your boiler will be continually short cycling (stopping and starting), because the temperature will rise very quickly as there is nowhere for the excess heat to go.
You said earlier that you calculated the heat requirement as about 13kW. Did you use the calculator I suggested and did you deduct the 2kW allowance for hot water?
Either way, it would appear that your radiators are seriously undersized. Does that agree with your experience?
I wonder why the previous owner put in undersized rads???I'm pretty sure I've chosen the right rad sizes from the catalogue, but I can double check. They are definitely the ones without the fins on the back. Unfortunately, they were brand new when we moved in, so I was loathed to replace them.
In that case you have a heating requirement of about 11kW but only about 4kW of rads. The boiler can modulate down to about 6KW.I calculated the heating requirement based on the calculator you linked me to, but I did not subtract the the DHW allowance.
What's the output of this? Was it there when you moved in? If so it could account for the undersized rads.I have a wood burner that takes over and causes the TRVs to shut.
Anyway, after checking the size and type of the rads PROPERLY, the outputs are 1200W and 800W. Therefore, the correct calculation is as follows:
(1200x4)+(800x3) = 7200W
Useful in the present very cold weather.Regarding the stove, it was something that I fitted when I moved in. Nothing to do with the heating output, I just always fancied having one and the cat/dog/missus love it! (I should watch how I write that!)
Output of stove is 8kW max.
Are you sure it's not the wall stat turning the boiler off before the rooms with TRVs have reached temperature?Seems to work well, but I need to get the TRVs set right, as they're going off a little early still.