In a current thread ( see here), I have been discussing some issues about Supplementary Bonding (SB) which, after years of not thinking so deeply about these things, have recently occurred to me. Since my conclusions seem to be considerably at variance with what BS7671 seems to imply, I’m not all that comfortable, and therefore would welcome and comments which may reveal flaws in my thinking.
In the meantime, my main current (tentative!) conclusions appear to be as follows:
Some of the above seems to be considerably at variance with the thinking (and requirements) of BS7671, so I would be very interested to hear any thoughts about the above, particularly if they reveal any flaws in my reasoning as discussed in the other thread.
My greatest concern is probably the implications of 701.415.2(vi) - which seems to be suggesting that (all other conditions being satisfied) SB can be omitted in the situation in which (by my reasoning) the risk from electric shock of the type I have described is at its greatest (‘severity’-wise).
I therefore have to question the validity of my reasoning, since I would not presume to suggest that I ‘know better’ than the many experts (or ‘experts’) who must have given their blessing to the regulation!
Kind Regards, John
In the meantime, my main current (tentative!) conclusions appear to be as follows:
- IF one wants to ensure that a situation cannot arise in which a dangerous potential difference can arise between simultaneously-touchable extraneous-c-ps and exposed-c-ps, or between simultaneously-touchable exposed-c-ps on different circuits, then:
- The only way of achieving that appears to be to install Supplementary Bonding, locally joining together all simultaneously-touchable extraneous- and exposed-c-ps
- Although BS7671 only (occasionally) requires SB in bathrooms, the above applies more-or-less equally to any room. The only small difference is that the severity of electric shock may be somewhat greater in a bathroom because of ‘wet skin’, but that is equally true in any room which has water (kitchens, utility rooms, bedrooms, toilets, bedrooms with hand-wash basins etc.).. Even with dry skin (hence in any room) there is a risk of severe electric shock if dangerous PDs can arise between simultaneously-touchable parts.
- 701.415.2(vi), which (via a Note) invokes the test criteria described in 415.2.2, implies that risk reduces (and hence SB may be omitted if all other conditions are satisfied) if the resistance from extraneous-c-p to MET is low. However, by my reasoning this is NOT correct. Indeed, on the contrary, it seems to me that the severity of shock will actually tend to (slightly) increase as that resistance decreases - with the risk of shock being as high as ever, and the severity of the shock (if it happens) being at its highest if that resistance became (hypothetically) 'zero'.
- IF, on the other hand, one decides that when there is RCD protection, there is no need to worry about the possibility of a dangerous potential difference arising between simultaneously-touchable extraneous-c-ps and exposed-c-ps, or between simultaneously-touchable exposed-c-ps on different circuits, then:
- there would seem to be minimal reason for requiring SB anywhere when there is RCD protection, thereby questioning the need to single out bathrooms as requiring SB (under certain circumstances).
- Other regulations in BS7671 already require that circuits supply bathrooms should be RCD protected and, indeed, that in the absence of RCD protection, SB must be installed in bathrooms.
My greatest concern is probably the implications of 701.415.2(vi) - which seems to be suggesting that (all other conditions being satisfied) SB can be omitted in the situation in which (by my reasoning) the risk from electric shock of the type I have described is at its greatest (‘severity’-wise).
I therefore have to question the validity of my reasoning, since I would not presume to suggest that I ‘know better’ than the many experts (or ‘experts’) who must have given their blessing to the regulation!
Kind Regards, John