Watch this space - I'm 'drawing'I'm not sure any more, but - .... how can there be a PD between exposed- and extraneous-c-ps if the resistance between them is negligible; either because of bonding or shortness of connections?
Kind Regards, John
Watch this space - I'm 'drawing'I'm not sure any more, but - .... how can there be a PD between exposed- and extraneous-c-ps if the resistance between them is negligible; either because of bonding or shortness of connections?
OK. Start with the simplest situation, which I presume is what you are thinking of, namely ...I'm not sure any more, but - how can there be a PD between exposed- and extraneous-c-ps if the resistance between them is negligible; either because of bonding or shortness of connections?
Yes, of course it wouldn't.Yes, that's alright as you have drawn it, but isn't the last statement agreeing with what I am saying - and the regulations? .... Surely with a bond between your A and C like this: .... would mean a person (assuming not earthed) touching Y and Z would not result in a shock any more than if touching W and X.
Oh, right. Have I been looking at the wrong bit?Yes, of course it wouldn't.
Yes. Edit - Z and Y; not Z and MET.However, surely the point is that if (without SB) you had measured a very small resistance between your Z and Y (or between Z and MET), you would have concluded that the bond was not required, wouldn't you?
I suppose so.If that were the situation, and your conclusion, such that you did not install any SB, you would have left the door open to a potentially lethal PD arising between your Z and Y (which might be 'simultaneously touchable'), wouldn't you?
Well, yes, but as I said before; you cannot dismiss a test as superfluous because it verifies a satisfactory result.Whatever, my question about the 'test' of 415.2.2 remains - what on earth is it attempting to achieve? As a test of the adequacy of SB which one had installed (which is seemingly what it is intended for) it is surely superfluous - since it's inconceivable that any bit of G/Y SB conductor would not satisfy the test, isn't it? - i.e. all one would be testing would be how well one had connected the G/Y.
You tell me - I'm not sure which 'bit' you have been looking atOh, right. Have I been looking at the wrong bit?
It doesn't really matter to this discussion, but I'm a bit confused by your 'edit' - I thought that you regarded a very low resistance between a 'part' and the MET as indicating that it did not need to be bonded?Yes. Edit - Z and Y; not Z and MET.
I'm afraid that I don't understand those questions. Could you perhaps clarify in a way that even I can understand?I suppose so. Then what would be the difference between touching two points at the same potential on a single conductor and your drawing? Maybe 49V instead of 1V - Is that the point?
As a test of the adequacy of SB which has been installed, I would say that it is not merely 'superfluous' but is actually potentially dangerous. In a situation in which two nearby conductive parts have theoretically been electrically connected by a short length of G/Y (usually of of ≥4mm² CSA) that 'test' would seemingly 'verify that the connection was satisfactory' if the measured resistance between the parts was as high as ~1,667Ω if RCD-protected and ~0.31Ω if only protected by a B32> The former would be totally ridiculous, and even the latter not a lot better (given that, say, 5m of 4mm² G/Y should have a resistance of only about 0.028Ω). Resistances so much higher than one would expect would presumably be indicative of very iffy connections which could well deteriorate with time.Well, yes, but as I said before; you cannot dismiss a test as superfluous because it verifies a satisfactory result.
Ok.Only one of my diagrams (the last one) is relevant. The fundamental difference between mine and your modification of it is that my diagram (and everything I have written) relates to the situation in which there is NO supplementary bonding in place.
Good.In your modification, you have added SB (i.e. a short bit of G/Y, usually of of ≥4mm² CSA, between extraneous-c-p and exposed-c-p) - which, as you say, would obviously ensure that the potential difference between those two parts would be close to zero under any credible circumstances.
No, that means it is an extraneous-c-p to the bathroom.It doesn't really matter to this discussion, but I'm a bit confused by your 'edit' - I thought that you regarded a very low resistance between a 'part' and the MET as indicating that it did not need to be bonded?
Well, I am not sure. Just trying to work out the regulation requirements.I'm afraid that I don't understand those questions. Could you perhaps clarify in a way that even I can understand?
Yes, but you know as well as I that the 1,667Ω (actually 1,666.66.; 1,667 is too high), like the 23,000kΩ, is just a nominal figure for 30mA and 10mA respectively.As a test of the adequacy of SB which has been installed, I would say that it is not merely 'superfluous' but is actually potentially dangerous. In a situation in which two nearby conductive parts have theoretically been electrically connected by a short length of G/Y (usually of of ≥4mm² CSA) that 'test' would seemingly 'verify that the connection was satisfactory' if the measured resistance between the parts was as high as ~1,667Ω if RCD-protected and ~0.31Ω if only protected by a B32> The former would be totally ridiculous, and even the latter not a lot better (given that, say, 5m of 4mm² G/Y should have a resistance of only about 0.028Ω). Resistances so much higher than one would expect would presumably be indicative of very iffy connections which could well deteriorate with time.
Fair enough - thanks for clarifying.No, that means it is an extraneous-c-p to the bathroom. For supplementary bonding I have always said measure between the exposed- and extraneous-c-p.
The resistance measurement obviously has to be undertaken when there is no fault. However, the rest of what I'm talking about (and depicting in diagrams) obviously relates to that "split second (or 5)" before the fault is cleared (assuming it is) by a protective device, since it's only during that very brief period that there is any possible 'dangerous potential' around to consider or worry about.Well, I am not sure. Just trying to work out the regulation requirements. Are you looking at the situation in a normal situation, rather than the split second (or 5) during a fault?
In the scenario I've been talking about, it would be at exactly MET potential (since no current flowing through the extraneous-c-p to MET, hence no VD). However, the exposed-c-p would be considerably above MET potential (144V above MET in my diagram) - hence a large potential difference between the two parts.What happens to the e-c-p potential during that fault?
[well, 0V above MET potential]With your hypothesis it would appear that SB is always required because, without it, the e-c-p is always going to be a 0V.
I don't think that makes 415.2.2 any less 'potentially dangerous' - because it could ('understandably) lead people to believe that ('required', for whatever reason, and present) SB was adequate when there was a "far too high" measured resistance between the extraneous- and exposed- parts, suggesting very poor connections.Yes, but you know as well as I that the 1,667Ω (actually 1,666.66.; 1,667 is too high), like the 23,000kΩ, is just a nominal figure for 30mA and 10mA respectively.
No - what makes you think that?I don't really know any more, but - Surely, during the period of the fault with many Amps flowing, the PD between the exposed- and extraneous-c-p is dependent on the impedance between them.
I suspect you may be trying to make it more complicated than it actually is - since it's really little more than Ohm's Law.Oh, I give up. You know voltage drop is not my favourite subject.
So, won't it happen in the CPC during the fault with, say, 160A flowing to the MET to which the extraneous-c-p is connected.I suspect you may be trying to make it more complicated than it actually is - since it's really little more than Ohm's Law.
There is only a voltage drop when current flows through a resistance/impedance, and the magnitude of the VD is then simply down to Ohm's Law.
Yes, but we are talking about fault currents.Hence, if one has a conductor through which no (or virtually no) current is flowing, then there will be no (or virtually no) voltage drop along it's length - i.e. the potential (relative to anything) will be the same at both ends of the conductor. That is the case with meter leads, the R1s in my diagram and the path via extraneous-c-ps to the MET.
In the fault situation I was talking about (L-E fault in a Class I item), the extraneous-c-p (or anything else connected to the MET) is irrelevant as far as the fault current is concerned. In the absence of SB, all of the fault current (160A or whatever) travels through the circuit's CPC to the MET, resulting in a large voltage drop along the length of that CPC (144V VD in my diagram, for a 2.5/1.5 mm² cable) - the voltage at the downstream end of that CPC (i.e. at the exposed-c-p) is therefor 144V (or whatever) above MET potential.One more try. .... So, won't it happen in the CPC during the fault with, say, 160A flowing to the MET to which the extraneous-c-p is connected.
Ah - you just beat me to it, since I was about to throw that very scenario at you!Ignoring the extraneous-cp, what would happen if you could touch the exposed-c-p and the MET when the fault occurred?
I assume that by "touch voltage" you're referring to the potential difference between the extraneous- and exposed- parts. Is that correct?Wouldn't the Touch Voltage be 160 x R of CPC? So the lower the resistance, the lower the TV. 160 x 0.3 = 48V would be ok. 160 x 1.0 = 160V not ok, so how to reduce? Reduce the resistance with bonding. So, isn't that the same, allowing for greater resistance, when instead touching the extraneous-c-p?