Boiler = Vaillant ecoTECplus418
Flow temp setpoint: 65°C
Anti-cycle time= 20mins
heat output: 18kW
bit of background - have a small bungalow, boiler generally worked fine with just the radiators (7 off them). i've since done an extension and added UFH with a manifold which is where the problems now are.
If I run the radiators for an hour, let them get up to temperature (and the boiler, set to 65°C flow) - then turn on the UFH manifold the boiler runs fine and controls to temperature. whole house works perfectly
If I turn on my entire CH at the same time (radiators + UFH manifold together) the boiler can never get out of it's start-up cycling phase. So it fires for roughly 1 min, get the flow up/above 65°C then turns off for 10 mins. then keeps doing the same thing. I'm assuming the boiler is trying to get the whole system up to temperature and a delta-T of about 20°C between flow & return before firing the boiler properly? When doing just the radiators this works, but adding in the mixed return of the UFH it just never gets there. 3 hours solid it won't get up to temp.
Is there a way to reduce this start-up cycle time? it doesn't seem to be linked to the anit-cycle time which I think is just relevant after the boiler is operting properly and up to temperature.
Flow temp setpoint: 65°C
Anti-cycle time= 20mins
heat output: 18kW
bit of background - have a small bungalow, boiler generally worked fine with just the radiators (7 off them). i've since done an extension and added UFH with a manifold which is where the problems now are.
If I run the radiators for an hour, let them get up to temperature (and the boiler, set to 65°C flow) - then turn on the UFH manifold the boiler runs fine and controls to temperature. whole house works perfectly
If I turn on my entire CH at the same time (radiators + UFH manifold together) the boiler can never get out of it's start-up cycling phase. So it fires for roughly 1 min, get the flow up/above 65°C then turns off for 10 mins. then keeps doing the same thing. I'm assuming the boiler is trying to get the whole system up to temperature and a delta-T of about 20°C between flow & return before firing the boiler properly? When doing just the radiators this works, but adding in the mixed return of the UFH it just never gets there. 3 hours solid it won't get up to temp.
Is there a way to reduce this start-up cycle time? it doesn't seem to be linked to the anit-cycle time which I think is just relevant after the boiler is operting properly and up to temperature.