That is certainly a possibility. I don't know when the standard for Type B MCBs was first created, and the crucial question is whether or not the 45% acceptable temporary overload for cables had been established by that time. No doubt someone will know the chronology of those two events.In view of the fact that cable has been around longer than mcbs, could it be that mcbs, when invented, had to be manufactured to these values to be able to be incorporated into an installation.
Well, an appropriate MCB has to be selected to adequately protect the cable, but the cable size in turn should have been determined according to the design current (i.e. load) - so we shouldn't really do things the way around you suggest. If one starts by selecting an MCB to suit then design current and then selects cable size on the basis of the In of the MCB, then one obvioulsy should end up in the same place - but it's still the design current that has really dictated the cable (and MCB)selection. What is not acceptable is to go for an MCB whose In is less than the design current, even if the cable is matched to that MCB.So it was the mcb that was matched to the cable even though now, apparently, we seem to be selecting cable to match the mcb.
Kind Regards, John