Have a guess at likely route of ring final. With power off remove two sockets one likely to on clockwise near to consumer unit, one likely to be on anti clockwise so you now have two sections.
One will go vir the CU, the other with be isolated from CU, with your tester find out which still has fault. You have now isolated the fault to a part of the ring final, depending on which section is next step, if fault seems CU side then again guess on a socket nearer to CU is not the aim centre of ring.
I am sure you can see the idea, if not then best you don't do the work.
One will go vir the CU, the other with be isolated from CU, with your tester find out which still has fault. You have now isolated the fault to a part of the ring final, depending on which section is next step, if fault seems CU side then again guess on a socket nearer to CU is not the aim centre of ring.
I am sure you can see the idea, if not then best you don't do the work.