Yes I can & it remains "On"
"It’s not usual to connect a cu to a ring circuit"
Why is that please ?
So the fault is downstream of the mini CU
There's me thinking it was an MCB!With the Mini Cu switched off can you reset the other RCD?
Except that a Ring Final Circuit (or a Radial Final Circuit) might be a final circuit in its own right but could have say a fused connection unit on it fusing down to yet another circuit (perhaps a light or three etc) , therefore the spur is a final circuit and is fed via its own distribution circuit (i.e. the ring/radial ) and that does not prevent it still being called a final circuit.The word final is important
In fact, BS7671 only mentions "Radial Final Circuit" three times, one being in ('informative') Appendix 15. It does, however, define a "Final Circuit',as "A circuit connected directly to current-using equipment, or to a socket-outlet or socket-outlets or other outlet points for the connection of such equipment." - and that could obviously apply to both a ring or radial circuit. ... and then,of course, we have "a orcuit" defined as electrical equipment supplied from the same origin and with a common OPD.A ring (or Radial) circuit is a final circuit as per the reg ...
Whilst that is all true, I don't think it is often a problem in practice. The only common situation in which one has (per BS7671 definitions) 'a circuit supplied by a circuit' is when there is an FCU, and I don't think many people regard what is downstream of an FCU to be 'a circuit' (whether final or otherwise). It's perhaps more 'difficult' when one has, say, a 'mini garage CU' fed from an OPD in a houses main CU.but it can have another working circuit on it that is also a final circuit and another and another final circuit on it but the ring or radial that it all springs from is still a final circuit in its own right. Plain English would not always allow such "sillyness" but our terminology does I`m afraid. I suppose that we could term some circuits ultimate and penultimate I suppose but I`m not sure that it would help much really.
Yep, I'm not aware of any possible types of circuits other than 'final' and 'distribution' ones, and I don't think that distribution ones would satisfy the BS7671 definition of a 'Final Circuit'. It defines a Distribution Circuit as "A circuit supplying a distribution board or switchgear." which I suppose is fair enough - but, interestingly in view of my comment about mini garage CUs above, it goes on to say "A distribution circuit may also connect the origin of an installation to an outlying building or separate installation, when it is sometimes called a sub-main." - so there's another bit of terminology for youI suppose that we use the word "Final" in RFCs to differentiate that it it not solely a distribution circuit so it must be a circuit with points on it.
Yes, In terms of literal wording of BS7671 definitions, a circuit could be both 'distribution' and 'final'. If it directly supplies current-using equipment, or has sockets etc. which could supply such equipment, then it is a 'final' circuit', but if it also supplies a DB ("or switchgear") it is also a 'distribution one'.So we might have 1/ Distribution circuits or 2/ Final circuits or 3/ A circuit that is both types at the same time, internal to an installation and we have distribution circuits that are external to an installation too. .... That, in essence, is what I was trying to explain/ A final circuit could be solely a final circuit or it could also be a distribution circuit to another (final?) circuit at the same time. Similarly we could have a distribution circuit that is solely such but we could also have one which is also a final circuit in its own right.
By considering things upstream of the origin of an installation, I think you are probably moving away from the scope of BS7671 and its definition. 110.1.1 of BS7671 ('Scope') starts by saying "The Regulations apply to the design, erection and verification of electrical installations such as those of:" (followed by list of 27 "such as" items !)(.And, my view is, a Ring or a Radial could equally be such final/distribution/ both in any installation and in any installation that is of the type we might call sub mains. .... External to an installation we tend to divide into distribution (being "fairly local") and Transmission (but not so much excluding generation) but , yet again, some might narrow down our two main bands of high/low into more like high/medium/low more akin to differing terms of generation/transmission/distribution.
Yes, I can pride that soon but am testing for continuity now.A photo of the mini cu could be helpful
No, have been testing continuity between rectification of car problems.Have you managed to locate a fault on the ring in your Mini CU?
@Murdochcat & ericmark. I have carried out continuity checks on the ring as you advised. there are no faults. All readings are between 0.3 & 0.6 ohms.These checks were repeated several times for my experience.Yes, I can provide that soon but am testing for continuity now.
[All readings are between 0.3 & 0.6 ohms.These checks were repeated several times for my experience.