I called the power distribution, they said a nice guy around within a couple of hours. He checked the readings with the clamp meter, and he agreeded it was unusual for current to be flowing through the earth bond with the mains off at 2.9A
As has been mentioned earlier, with TN-C-S and solid metallic links between properties by way of other services, that really isn't an exceptionally high current to see flowing if there's a fair load in other neighboring properties at a particular moment in time. John mentioned the point about 3-phase distribution, which is what's found feeding most homes in Britain, and how loads balanced across the phases cancel out the overall neutral current. If you applied identical loads to each phase, the neutral current back to the transformer would be nil, regardless of how high those loads were, so maximum overall neutral current is not necessarily highest when the total load is at its highest, it depends more upon the distribution of the load across the phases. But in the situation we're looking at here, it's more complicated than that anyway, since while in a perfectly balanced system with identical loads on each phase the neutral current at the transformer will be nil, there will still be various magnitudes of current flowing in different sections of the neutral in the distribution system depending upon the precise location and size of each home's load, and there will be parallel paths by way of the bonded services between numerous different points of the distribution system's neutral.
I wonder if the guy who looked at your installation is more used to seeing installations where there are
no solidly connected services between buildings, in which cases you would expect any current through the bonding to be considerably lower.
He also said he wan't sure why there should be an earth bond connecting from the previous TN-S earth sheath and the TN-C-S earth & neutral PEN.
For the reasons which were outlined earlier - He really should know that.
He disconnected all the earths, and the current stopped, if he connected my main earth bond to the TN-C-S it started again
All of which is perfectly normal. As soon as you connect your bonded services to the incoming neutral, you've created the parallel path through which
some portion of the distirbution system's neutral current can flow. The exact proportion depends upon the relative resistances.
He said my installation was within normal readings, but said if we wanted the equipment could upgraded for the PME.
I would hope that all the necessary work had already been done as you've already been connected as such.
He wasnt able to disconnect the earth bond between the TN-S and the TN-C-S because he wasn't sure if they were there for a unknown reason, and he naturally could not disconnect my main earth bond. He said the issue was interesting and unusual for him, and wasnt sure what it could be, but thought to be an issue with the earth wiring on our side than the distribution.
Not sure what others might think, but adding all these observations about him up, it sounds as though he's perhaps a little inexperienced or doesn't really understand the situation.
Later after gone i decided to investigate the main water earth bond. We have a plastic join on our water main for our SureStop water switch, so we have our main exponential water bond below that, and a wire linking between the part of copper water main and the rest of the water piping in the house.
I think you meant "equipotential."
Anyway, so it sounds as though you definitely have a bond to a metallic underground water service line. If they were all built at the same time, there's a fair chance that your neighboring houses have the same, and if those pipes are all solidly connected (electrically) to a metallic water main in the street, you have an interlinked web of parallel connections across various parts of the distribution neutral by way of every home which is arranged as TN-C-S. There is no way you will ever prevent
some current from flowing through your bonding and pipework in this situation.