OK. I'll try to do this without a diagram ...

... think of having R1 and R2 in series with 230V applied across the two of them, through a fault (a dead short) between them at the end. The same ('fault') current flows through both of them, so the voltages across the two resistances will be proportional to those resistances (Ohm's Law - voltage across each resistance = resistance x current). Hence, if there is 50V across R2 and 230V across (R1+R2), then:

50/230 = R2 / (R1+R2)

after which it's just a little simple algebra ....

50 x (R1+R2) = 230 x R2
then (omitting the multiplication symbols for simplicity) ...
50R1 + 50R2 = 230R2
50R1 = 230R2 - 50R2
50R1 = 180R2
R2 = (50 / 180)R1
R2 = 0.28R1 (approx)
hence R2 is approx 28% of R1

... can you follow that?

Kind Regards, John
 
Yes, bond them together V=I(p)xR.
20Ax0.01Ω=0.02V 20Ax0.1Ω=2V 20Ax1Ω=20V 20Ax2.5Ω=50V
390Ax0.01Ω=3.9V
Bond what to what?

One can obviously minimise potential differences ('touch voltages') between two exposed-c-ps, or between an exposed-c-p and something else which was 'earthed' (like a pipe) by connecting them together with a bonding conductor, but to apply that approach generally would require a local bonding conductor ('SB') between every exposed-c-p and every other simultaneously touchable exposed-c-p or 'earthed' item - which would not really be very practical, would it?

Kind Regards, John
 
My turn now (and it ain't 'not visible to normal visitors' any more :) ) !!!

upload_2020-2-6_19-41-10.png
 
upload_2020-2-6_19-43-39.png


The voltage between e-c-ps - exposeed and extraneous - is what touch voltage refers to but we only have to consider it in bathrooms etc. when you might be earthed (effectively).

Obviously a live exposed-c-p is always at 230V.
 
Ah, I now see what 'C' in Studentspark's diagram is.

The 23,000Ω, including body resistance, to the MET is the value above which parts are not considered to be an extraneous-c-p - although, as the voltage is likely to be 240V, 24,000Ω is more realistic.

This limits the touch voltage to 10mA below which is not considered dangerous so the figure in the diagram is 0.01A - 10mA.

Having said that some like to limit it to 5mA so a value of 48,000Ω will be used - although it is a compromise between the two.
 
The voltage between e-c-ps - exposeed and extraneous - is what touch voltage refers to but we only have to consider it in bathrooms etc. when you might be earthed (effectively).
It that qualification relevant? - if you are talking about the p.d. between two conductive parts, then whether or not one 'might be earthed' is surely irrelevant (or, at least, 'different'), isn't it?
Obviously a live exposed-c-p is always at 230V.
Not if it is an exposed-c-p which is connected to an 'effective' CPC. That's what I've been talking about (and doing calculations about) - the potential that would exist on a (CPC-connected) exposed-c-p if L came into contact with it.

Kind Regards, John
 
It that qualification relevant? - if you are talking about the p.d. between two conductive parts, then whether or not one 'might be earthed' is surely irrelevant (or, at least, 'different'), isn't it?
Yes you are right. I only added it afterwards for some reason trying to think of everything at once.

Not if it is an exposed-c-p which is connected to an 'effective' CPC. That's what I've been talking about (and doing calculations about) - the potential that would exist on a (CPC-connected) exposed-c-p if L came into contact with it.
Probably not. I was trying to think of the example fault taking a long time to clear.
 
It that qualification relevant? - if you are talking about the p.d. between two conductive parts, then whether or not one 'might be earthed' is surely irrelevant (or, at least, 'different'), isn't it?
I should have said 'unless' you are earthed when it (touch voltage) makes no difference. I think. :)
 
Probably not. I was trying to think of the example fault taking a long time to clear.
When you wrote "Obviously a live exposed-c-p is always at 230V" you were presumably thinking of a situation in which not only was the exposed-c-p connected to L, but also in which it had lost its connection to an effective CPC. If one considers 2.5mm²/1.5mm² T+E then, even if there are no 'parallel paths', if the CPC is still connected the potential of the exposed-c-p will only be about 142V (about 62% of 230V), and if there are parallel 'earth' paths it will be less than that.

Kind Regards, John
 
Yes, I knew you'd get it in the end. :LOL:

I'm going in the bath now. No exposed nor extraneous-c-ps in the room. :)
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top