I didn't initially realise that you were talking about 'two faults' (L in contact with exposed-c-p and no CPC connected to it)!Yes, I knew you'd get it in the end.
Kind Regards, John
I didn't initially realise that you were talking about 'two faults' (L in contact with exposed-c-p and no CPC connected to it)!Yes, I knew you'd get it in the end.
That's an interesting point. Not surprisingly, all of my bathrooms have things which are potentially extraneous-c-ps (pipes etc.) but none of my bathrooms, nor any of those I commonly frequent, have any exposed-c-ps (except, possibly, some above-zones, and certainly not touchable, light fittings) - which leads me to wonder (in view of all the discussions about SB etc.) how common it actually is for bathrooms to have any touchable exposed-c-ps?I'm going in the bath now. No exposed nor extraneous-c-ps in the room.
To be honest I wasn't.I didn't initially realise that you were talking about 'two faults' (L in contact with exposed-c-p and no CPC connected to it)!
I think most people who discuss the subject, usually forget about the 'simultaneously accessible'.That's an interesting point. Not surprisingly, all of my bathrooms have things which are potentially extraneous-c-ps (pipes etc.) but none of my bathrooms, nor any of those I commonly frequent, have any exposed-c-ps (except, possibly, some above-zones, and certainly not touchable, light fittings) - which leads me to wonder (in view of all the discussions about SB etc.) how common it actually is for bathrooms to have any touchable exposed-c-ps?
Fair enough, but ...To be honest I wasn't.
... is not the answer that such will not happen if (assuming TN) the circuit has been designed to have an adequately low Zs and the exposed-c-p is still connected to the circuit's CPC?More trying to explain or work out (as in Studentspark's example) the unlikely situation where an earth fault, for some reason, takes a long time to clear or does not clear at all.
That's very probably true but 'worse' than that, as I said, none of the bathrooms with which I am familiar have any exposed-c-ps at all - and I imagine that the same is true of many/most bathrooms (other than, in some cases, Class I light fittings on the ceiling that one would need a stepladder to be able to touch) - electrically-heated towel rails are perhaps about the most likely possessors of exposed-c-ps in a bathroom, but I can't think of any bathroom I know which has one of them.I think most people who discuss the subject, usually forget about the 'simultaneously accessible'.
Eh? That seems to be very 'trigger happy'. He was still 'here' about three hours ago and, judging by what he then wrote, has gone away to think about what I wrote in my (then) previous post (and I strongly suspect 'will be back') ...MOD: FYI The OP has left the conversation.
Thank you. I'll need to read it a few times. Really appreciate your help
MOD: FYI The OP has left the conversation.
50/230 = R2 / (R1+R2)
after which it's just a little simple algebra ....
... or even less. It's obviously arbitrary but, in terms of most things (the calculations we're talking about, the definition of ELV etc.) it was decided that 50V AC was a reasonable dividing line below which the chance of a serious/fatal shock was very low (and I'm personally inclined to agree that that is a reasonable threshold) , and that sort of thinking seems to persist today. For example, the HSE currently say things like...I am not sure when 50 volt AC was decided as the limit for live items you can touch? With salt on road vehicles you can still get a tingle with 24 volt DC ...
... A voltage as low as 50 volts applied between two parts of the human body causes a current to flow that can block the electrical signals between the brain and the muscles....
.. and even with a 1.5V battery - but, to be fair, the unpleasantness of that experience is at least as much to do with electrolysis of saliva as to 'electric shock'.My daughter as a very young child was found licking the terminals of a PP3 battery.
You're presumably talking about RCD tripping as a result of an L-CPC fault, rather than a current through a person. With a 1kΩ rod resistance, the RCD would trip with a CPC voltage of 30V, but I'm not sure how that is likely to arise in practice - the nature of 'faults' is that it's likely to be '230V or nothing'. In the case of a current going through a person from L to CPC, then any rod resistance less that 6kΩ-7k (7,667Ω minus body resistance) will facilitate an RCD trip.I know the old ELCB-v was set to trip at 50 volt, but I personally think that is rather high, it is rare to find 10 volt never mind 50. All formulas already given, but some times you have to use some common sense, even if the earth rod will work a RCD at 1kΩ, we know that is unreliable, think book says 300Ω but personally would not accept over 60Ω.
If, for convenience, we take R1 as 1Ω, then, with that ratio, R2 is 1.67Ω.
Hi. Although it says that you posted this at 19:57 yesterday, it has only appeared for me in the last few minutes! I just wanted to let you know that I'm not ignoring you, and will try to help you with your knots shortly!Thanks for all your time and the replies, Ive given it some thought...
But I totally understand if you want to give this one up as a lost cause. I am getting myself ties up in knots...
For a start, I'm not sure where your starting figures come from. The maximum Zs for a B32 is 1.37Ω and, per BS7671, 1.5mm² cable is 14.5 mΩ/m (at 70°) and 2.5mm² cable is 9 mΩ/m (at 70°). However, that doesn't alter the concept of your calculations.Thanks for all your time and the replies, Ive given it some thought...
But I totally understand if you want to give this one up as a lost cause. I am getting myself ties up in knots... Well I took that example, and put in numbers that would satisfy Zs requirements ...
Hi. Although it says that you posted this at 19:57 yesterday, it has only appeared for me in the last few minutes! I just wanted to let you know that I'm not ignoring you, and will try to help you with your knots shortly!
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local